SJOOW For Welder: What gauge?

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
I've got a small 220v MIG welder I need to move around my garage and maybe even outside. The spec sheet says 20A, I am pretty sure I read FLA=26A somewhere.

I have a dryer outlet located within 25 feet of the panel, protected by a 30A breaker and fed by 10/4 romex.

My original plan was to get a 50' 8/3 pre-made extension cord, or get a length of 10/4 SJOOW and make one. Was asking around at work today for the opportunity to purchase (we buy multiple huge rolls) and it was suggested that 8 gauge is overkill.

I'm playing around with some online calcs tonight and it seems like 10 gauge is adequate for over 75ft (25 from breaker, 50 cord), in fact I can go 150ft and still not see a 5% drop.

What am I missing here? Does an outlet need to be factored in somehow? I have no issues running 8 if it makes a big difference, but wouldn't mind saving some money if I can run 10 gauge.
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,517
Location
SE MI
I would use 10-3 SO. It has a thicker jacket than SJ.

True, but if there was more than a 10% difference, I would buy the SJOOW.

10/3 would be fine for 50'. Welders typically have a low duty cycle (<50%) so you can use a slightly smaller cable. Extension cords are typically "upsized" 1 gauge compared to permanent wire.

If you wre going to pull close to 30A continuously, I would go 8/3.

You don't need a neutral if you are only using the extension for 240V.
 
OP
P

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
You don't need a neutral if you are only using the extension for 240V.

I am aware, but hadn't decided the best way to transition from the dryer outlet with neutral to the welder. Can I safely just pull off the 2 hots and ground, or should I make a short whip (dryer plug to welder plug) where I bond the neutral and ground?
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,788
I am aware, but hadn't decided the best way to transition from the dryer outlet with neutral to the welder. Can I safely just pull off the 2 hots and ground, or should I make a short whip (dryer plug to welder plug) where I bond the neutral and ground?

NO! NO! NO! NO! The neutral & grounding conductors are never bonded past the service equipment.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Make the cable "right" and you can use it for a generator extension cord also.

Use L14-30 twist locks on each end, and if needed, make a adapter to the welder plug configuration or change the welder plug to match.

I got lucky and found two pieces of new 8/4 SOOW local from a CL seller for $100 (said it was in a van he bought from a HVAC repairman along with a bunch of other junk ). One piece, after trimming and installing ends is 37 ft the other is 45 ft. Found the ends on Ebay, $10 each shipped for new female Bryant/Hubbell ends and $25 for a lot of 4 ea individual plastic hard pack, of the male ends, Pass & Seymour. Used one of the spare male ends to make a short cheater cord to transition to my welder plug.

Charles
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
You can use a 12-3 if you want but 10 is ideal even for some larger machines. Since this is a home brew deal anyway why make a bunch of froggy adapters, get a cord, put a dryer on one end and welder on the other.

Can I safely just pull off the 2 hots and ground,
Not only can you but it is the way is should be done.
 