Smaller wire int larger lugs
Joemctag
Outside raleigh nc
Can I safely terminate 2 gauge Al conductors in lugs apparently made for 4/0 ?
Setting up a used mobile home. Temporary. Not inspected.
Planning on coming off main 200A panel in shop, using a 100A breaker feeding 120’ of 2-2-2-4 MHF underground to 200A panel inside mobile home.
Also, decided not to put a disconnect outside the mobile home. I’d like to, however, post a durable sign stating that the building ( mobile home ) is fed by the shop so many feet southeast. ( Its meter is clearly visible ). What’s the best, most correct way for that to read?
beemerphile
Danielsville, GA USA
Most lugs have both a min and max rating. I have some Square D lugs I'm looking at that are rated 1 AWG - 4/0. These would not be appropriate for a 2 AWG wire. Maybe some others are. I don't know how to interpret the "best, most correct" way to do something that wouldn't pass an inspection. Beginning in 2020 NEC 230.85 requires a readily accessible exterior emergency disconnect. Prior to that many local authorities had an exterior disconnect requirement under other life safety guidelines. I think NC is under the 2020 NEC. It would not be too expensive to sink a 6x6 post outside the MH and mount a disconnect there.
mike93lx
Richmond, VA
Polaris makes a connector that will go from #6 to 250mcm, so you could use them to just up in wire size.
Or something like this
J
Joemctag
Outside raleigh nc
I was actually all ready to do that and noticed that although my incoming 4-4-4-2 MBF to my 100A breaker in my exterior disconnect cabinet would fit nicely in the breaker’s lugs, my 4/0s coming from the mobile home’s panel were too big for the 100A breaker’s lugs. I wasn’t going to ask if it was ok to just cut off some of the 4/0’s aluminum strands so it would fit.
Someone else just posted that there are splice lugs to do what I want to do. I guess they either bolt inside the cabinet with insulators or you have them loose and wrapped with electrical tape? Will go look at some.
mike93lx
Richmond, VA
You wrap them. With a lot of tape.
That's one thing that is nice about the Polaris connectors. They are fully insulated so no messing around with tape in a tight box and with thick conductors. Tighten down and you are done
J
Joemctag
Outside raleigh nc
Thanks! If I can’t get them at Lowes or my electrical supply, I’ll order some online.
alfredeneuman
Fullerton, CA
The pin terminals pictured require a special crimper to install them, only available from the manufacturer of the crimp. The crimper is too expensive for a 1 time installation.
(I think they also come in a set-screw configuration too)
ZX3ST
STL
Someone will correct me if I am wrong on this but I think #2 MHF is only good for 90A so you need a smaller breaker or bigger wire.
You'd be correct if this were a subpanel application in which you must make some different assumptions on load.
As a main feeder, it's fine for 100A.
This is why many people get confused when running #2 MHF to subs, because the supply house assumes you're using as a main feed, and tell you it's good for 100A.
EDIT: Apparently I can't read...... Sorry. 90A rating in this application.
what wire range are the lugs listed for?