Smaller wire int larger lugs

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
Can I safely terminate 2 gauge Al conductors in lugs apparently made for 4/0 ?
Setting up a used mobile home. Temporary. Not inspected.
Planning on coming off main 200A panel in shop, using a 100A breaker feeding 120’ of 2-2-2-4 MHF underground to 200A panel inside mobile home.
Also, decided not to put a disconnect outside the mobile home. I’d like to, however, post a durable sign stating that the building ( mobile home ) is fed by the shop so many feet southeast. ( Its meter is clearly visible ). What’s the best, most correct way for that to read?
 
To avoid these ads, REGISTER NOW!

beemerphile

Well-known member
Joined
Jul 9, 2021
Messages
727
Location
Danielsville, GA USA
Most lugs have both a min and max rating. I have some Square D lugs I'm looking at that are rated 1 AWG - 4/0. These would not be appropriate for a 2 AWG wire. Maybe some others are. I don't know how to interpret the "best, most correct" way to do something that wouldn't pass an inspection. Beginning in 2020 NEC 230.85 requires a readily accessible exterior emergency disconnect. Prior to that many local authorities had an exterior disconnect requirement under other life safety guidelines. I think NC is under the 2020 NEC. It would not be too expensive to sink a 6x6 post outside the MH and mount a disconnect there.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,962
Location
Richmond, VA
Polaris makes a connector that will go from #6 to 250mcm, so you could use them to just up in wire size.

Or something like this


 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
Most lugs have both a min and max rating. I have some Square D lugs I'm looking at that are rated 1 AWG - 4/0. These would not be appropriate for a 2 AWG wire. Maybe some others are. I don't know how to interpret the "best, most correct" way to do something that wouldn't pass an inspection. Beginning in 2020 NEC 230.85 requires a readily accessible exterior emergency disconnect. Prior to that many local authorities had an exterior disconnect requirement under other life safety guidelines. I think NC is under the 2020 NEC. It would not be too expensive to sink a 6x6 post outside the MH and mount a disconnect there.
I was actually all ready to do that and noticed that although my incoming 4-4-4-2 MBF to my 100A breaker in my exterior disconnect cabinet would fit nicely in the breaker’s lugs, my 4/0s coming from the mobile home’s panel were too big for the 100A breaker’s lugs. I wasn’t going to ask if it was ok to just cut off some of the 4/0’s aluminum strands so it would fit.
Someone else just posted that there are splice lugs to do what I want to do. I guess they either bolt inside the cabinet with insulators or you have them loose and wrapped with electrical tape? Will go look at some.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,962
Location
Richmond, VA
I was actually all ready to do that and noticed that although my incoming 4-4-4-2 MBF to my 100A breaker in my exterior disconnect cabinet would fit nicely in the breaker’s lugs, my 4/0s coming from the mobile home’s panel were too big for the 100A breaker’s lugs. I wasn’t going to ask if it was ok to just cut off some of the 4/0’s aluminum strands so it would fit.
Someone else just posted that there are splice lugs to do what I want to do. I guess they either bolt inside the cabinet with insulators or you have them loose and wrapped with electrical tape? Will go look at some.
You wrap them. With a lot of tape.

That's one thing that is nice about the Polaris connectors. They are fully insulated so no messing around with tape in a tight box and with thick conductors. Tighten down and you are done
 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
You wrap them. With a lot of tape.

That's one thing that is nice about the Polaris connectors. They are fully insulated so no messing around with tape in a tight box and with thick conductors. Tighten down and you are done
Thanks! If I can’t get them at Lowes or my electrical supply, I’ll order some online.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,595
Location
Fullerton, CA
The pin terminals pictured require a special crimper to install them, only available from the manufacturer of the crimp. The crimper is too expensive for a 1 time installation.
(I think they also come in a set-screw configuration too)
 
Last edited:
To avoid these ads, REGISTER NOW!

ZX3ST

Well-known member
Joined
Jun 6, 2015
Messages
163
Location
STL
Someone will correct me if I am wrong on this but I think #2 MHF is only good for 90A so you need a smaller breaker or bigger wire.
You'd be correct if this were a subpanel application in which you must make some different assumptions on load.

As a main feeder, it's fine for 100A.

This is why many people get confused when running #2 MHF to subs, because the supply house assumes you're using as a main feed, and tell you it's good for 100A.

EDIT: Apparently I can't read...... Sorry. 90A rating in this application.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
Can I safely terminate 2 gauge Al conductors in lugs apparently made for 4/0 ?
Setting up a used mobile home. Temporary. Not inspected.
Planning on coming off main 200A panel in shop, using a 100A breaker feeding 120’ of 2-2-2-4 MHF underground to 200A panel inside mobile home.
Also, decided not to put a disconnect outside the mobile home. I’d like to, however, post a durable sign stating that the building ( mobile home ) is fed by the shop so many feet southeast. ( Its meter is clearly visible ). What’s the best, most correct way for that to read?
what wire range are the lugs listed for?
 