Trying to figure out what service I need to plan for.

Building will be something less than 800sq ft., a 24 or 26x30, or a 24x40 if my tax refund is good this year.

Utilities guy says I can get a 320amp meter at the house, and have 125, 150 or 200 at the shop, or have a 100amp service run off the existing meter.

I have a large 80gal compressor and two welders (MIG and TIG). I know the compressor draws something like 40 - 50 amps at startup. It would make the lights dim for a second at my old shop (100amp service) but never popped the breaker. Welders, maybe 20 amps each.

Not sure how to plan for lights and outlets. Probably have two breakers for the lights and one for every two outlets. Let me know if this is overkill.

It will be a one-man shop, so the likelihood of having more than one high-current consumer going at once is kinda slim.
 
To avoid these ads, REGISTER NOW!

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
It is difficult to assess your needs without knowing more about how you use things. I'm guessing it would be very unlikely that you would be welding with both welders at the same time.
I can't see a 1 man shop coming up short on power with 100 amp service unless you have some really huge power hog tool.
I have 100 amp service in my garage. I have 2-240v heaters for winter, and a 5hp 240v compressor. I have 30 receptacles and 14 lights, and I never come up short on power. I don't use the compressor often when both heaters are running, but with 100 amps, there is enough to handle them all.
My compressor wants 22 amps. My two heaters want about 38 amps. Even with that load, I don't get dimming of the lights when the compressor starts.
In my experience, dimming of the lights comes from wire runs that are long enough to start reaching the limit of the wire size used on the main circuit.
Try to keep your wire runs as short as possible, and if you are near the limit of the wire, upsize it one size.
My 100 amp service is on #2 copper.
My 120v small compressor is on a 20A circuit and #10 copper wire.
My 240v compressor is on a 30A circuit and #8 copper wire.
This seems to eliminate dimming of lights on other circuits.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Sounds to me a 100A will do. Two circuits for lights is fine, but I'd put more than 2 outlets on a circuit. I'd put at least 4 outlets on a circuit, but that's me.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I have never seen a common garage of this nature trip a 60 a breaker on a 2 aluminum wire. Even with regular daily use of 5 hp comp.
 
OP
D

D-fens

Well-known member
Joined
Nov 9, 2013
Messages
109
Thanks for the input.

I was a little skeptical of the electrician guy trying to sell me 200amp service.
 

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757
Trying to figure out what service I need to plan for.

Building will be something less than 800sq ft., a 24 or 26x30, or a 24x40 if my tax refund is good this year.

Utilities guy says I can get a 320amp meter at the house, and have 125, 150 or 200 at the shop, or have a 100amp service run off the existing meter.

I have a large 80gal compressor and two welders (MIG and TIG). I know the compressor draws something like 40 - 50 amps at startup. It would make the lights dim for a second at my old shop (100amp service) but never popped the breaker. Welders, maybe 20 amps each.

FWIW, the most likely cause for those lights dimming every time the compressor kicked on was NOT inadequately-rated service to the building, per se; but rather, you were probably inducing some significant voltage drop due to too-long runs of not-quite-big-enough (but still "legal") wiring.

In any event, those two items (compressor & welders) are very probably two of the three major variables which need to be considered (see below for the third); and you need to presume that from time to time you WILL be welding when the compressor happens to kick on. Also, with that much compressor and two welders, can a plasma cutter be far behind?

Not sure how to plan for lights and outlets. Probably have two breakers for the lights and one for every two outlets. Let me know if this is overkill.

Splitting the lights up into two separate circuits is a good idea, even if it's not strictly "necessary" based just on the load. That way, if/when one trips (or needs to be shut down to work on something), you're not left completely in the dark. When it comes to the switching for those lights, it should be well more than two circuits; but that's a separate discussion, really.

HOWEVER... Putting only two 120V outlets on each branch circuit is DEFINITELY overkill. And here is why:

It will be a one-man shop,

This is the third major variable I spoke of. And given this, the odds on you needing more than two general-purpose 120V outlet circuits to cover the whole garage are somewhere between "slim" & "none". To this, I probably would add an additional 120V circuit for the workbench area itself (since that area typically becomes a magnet for all manner of plug-in "stuff"), and also dedicated (or at least "semi-dedicated") circuits for any 120V stationary machines with particularly heavy draws (such as table/band/miter saws, heavy-duty bench grinders, etc.). Also, putting the garage door opener(s) on a dedicated circuit is generally a good idea. But in all of these cases, those extra circuits would be there more "on general principles" than because they'd really be NECESSARY in a one-man shop.

Setting aside the "special" circuits for a moment, those two "main" 120V circuits should be run TOGETHER, to double-gang outlet boxes spaced at perhaps 6-8 foot intervals all around the shop, with the bottom of the boxes at least 50 inches or so off the floor. In each of those double gang boxes, put two high-quality duplex outlets, one powered from each of the two circuits I just spoke of. The FIRST duplex in each of these "chains" must be a GFCI type, which (when properly installed) will also provide GFCI protection for all of the outlets "downstream" of the GFCIs.

so the likelihood of having more than one high-current consumer going at once is kinda slim.

See above for two possible exceptions to that; and if you do eventually get a plasma cutter, it goes beyond "possible" -- the compressor and the plasma cutter WILL be running concurrently.

Still, all told, I'd wager heavily that 90-100 Amp service will be quite sufficient for everything we've discussed thus far, unless that compressor is SUCH an inefficient old beast as to be well worth replacing just for this reason. Given that (and pending to some degree on the distance between the house and the shop), running some 2-2-2-4 MHF from your existing main service panel (presumably at the house), out to a moderate size (nominally "100-150A", depending on how many branch-circuit slots you want) sub-panel in the shop, will be your most cost-effective solution. You don't need a separate feed off the meter pan UNLESS there is no workable way to feed from the main service panel. In either case, you WILL need a 90A (not 100A) breaker at the main service panel (or in a separate disconnect box, if you tap directly into the meter) to protect the sub-panel feeder. You will also need a back-fed "Main" breaker rated at at least 90A (100A or more would be OK) in the sub-panel, to act as the "Local Disconnect".

The one thing which MIGHT cause me to re-think the "90-100 Amp" recommendation is if you were to put a large air conditioning system and/or electric space heat in that shop (gas- or oil-fired heat would be no problem, even if it has a substantial blower fan). But even this, in an ~800 ft.^2 shop, is not likely to make all THAT much difference, as long as said shop is well insulated.

I have never seen a common garage of this nature trip a 60 a breaker on a 2 aluminum wire. Even with regular daily use of 5 hp comp.

I think 60A is more than a little optimistic, in this case. Sure, he MIGHT "get away with it"; but that should not be the criteria for designing a new service installation.

Thanks for the input.

I was a little skeptical of the electrician guy trying to sell me 200amp service.

As well you should be.

Even presuming ALL of the "maybe someday" items (plasma cutter, HVAC, etc.), it's difficult to imagine you needing anywhere near that much juice. Heck, as long as this remains a one-man shop, even 125A would be overkill for what you're currently planning on; and would still be nearly overkill even considering the "maybe somedays".

 
OP
D

D-fens

Well-known member
Joined
Nov 9, 2013
Messages
109
Wow. Thanks 2ManyProjects.

The service to the shop will be something like 110 - 115ft (best I could measure without having any corner stakes up).

A plasma cutter isn't really in the budget right now but yeah, maybe when my checkbook recovers from all this.

Would like to add some form of HVAC within the next couple years, when and if it would be a window unit (24x30) or a small heat pump (24x40) because my neighborhood is all electric.

Planning on at least R12 in the walls and R22 or blow-in insulation in the attic. Probably going to drywall the inside because I don't like how the texture on OSB traps dust (I paint sometimes).
 
Last edited:

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757
Wow. Thanks 2ManyProjects.

You're quite welcome.

The service to the shop will be something like 110 - 115ft (best I could measure without having any corner stakes up).

Is that the TOTAL wiring run, or just the distance between the buildings? If the former, you'll be OK with Aluminum 2-2-2-4 MHF. If the latter, and we have to add more than about ten feet on each end to account for the verticals and snaking around to make the connections, then it starts to get marginal even for 90 Amps.

A plasma cutter isn't really in the budget right now but yeah, maybe when my checkbook recovers from all this.

Understood. But NOW is the time to make sure you have adequate electrical service to support that (and whatever else might be on the "Wish List"), if and when.

Would like to add some form of HVAC within the next couple years, when and if it would be a window unit (24x30) or a small heat pump (24x40) because my neighborhood is all electric.

Hmmm... All-electric heat MIGHT skew things a bit. Granted, a heat pump would be one of the more efficient ways to implement this; but they don't work well at very low ambient temperatures. That generally makes them less than ideal for typical shop/garage applications (where most of the time you just want to maintain low, but reliably above-freezing temperatures). That in turn means you'd PROBABLY be using the heat pump's auxiliary resistance heat a greater percentage of the time than would be the case for a typical residential application.

A window air conditioner running in Reverse Cycle mode is the same thing as a heat pump, only worse.

Planning on at least R12 in the walls and R22 or blow-in insulation in the attic.

When if comes to insulation, more is ALWAYS better. The more insulation you install now, the further out you push the break-even point; but in the long run, it's that much more FREE MONEY. And to quote Jimmy Fallon, "Who doesn't like free money?"

While we're on the subject... Has the slab been poured yet? I'm guessing not, which gives you a "Golden Opportunity" to optimize things for your future HVAC needs, AND take the pressure off the electrical service in the process...

First, regardless of anything else, insulate the utter living He__ out of that slab. Exactly what that constitutes will depend in part on your local climate (Hint: Where are you located?). But no matter what the locals might consider "normal", DO MORE. For example, I live in a fairly moderate Mid-Atlantic climate; and if I were building my house/garage today, I would have AT LEAST six inches of high-density polyisocyanurate foam under the slab. Note that the thermal break between the slab itself and the footers is also crucial to maintain good performance; so don't overlook this.

Secondly, if you can possibly swing it, bite the bullet and have PEX tubing installed in the slab when it's poured. If need be for budget reasons, you can stop there for now, leaving the loop ends run wild (and a little long) in the approximate location where the manifold will later be installed. This will set you up for in-floor hydronic heat, which is BY FAR the best (and most efficient) way to heat a shop/garage. The large radiating surface and high thermal mass of the slab is PERFECT for maintaining those "low but well above freezing" temperatures, at very low operating cost. Further, the "original heat source" for that system can be a moderate size high-efficiency domestic water heater, which will both help keep the electrical demands under control AND not compromise the indoor air quality/cleanliness. The heating system itself would be driven by a small circulator pump, which in turn would be controlled by the wall-mounted thermostat. When the 'stat calls for heat, the pre-heated cache of water in the tank will then be pumped through the system, to be replaced by the cold(er) water coming out of the floor. Presuming an adequate tank size vis-a-vis the total volume of water in the tubes, this will not excessively diminish the temperature of the water in the tank, making recovery a relatively quick (and low-load) proposition.

Probably going to drywall the inside because I don't like how the texture on OSB traps dust (I paint sometimes).

All the more reason for a heating system which does NOT rely on blowing air (and all the dust & guck it inevitably carries) around to do its job.

 
Last edited:
To avoid these ads, REGISTER NOW!

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I have never seen a common garage of this nature trip a 60 a breaker on a 2 aluminum wire. Even with regular daily use of 5 hp comp.

Mill, drill press, lathe, 3.5 HP compressor, 5kW heater, welder, two AC units, 42" TV, golf cart charger, etc, etc, 960 sq/ft - 2-2-2-4 AL MHF, 115' run, 70A breaker, no issues.
 
OP
D

D-fens

Well-known member
Joined
Nov 9, 2013
Messages
109
I'm in Huntsville AL. We have the benefit of relatively short, not-that-cold winters, but summertime heat indexes here can be brutal. A cool concrete floor is kind of nice in July or August.

For the near term I'm thinking a couple 48" or 60" ceiling fans. Also have a 3 burner propane heater (keep in mind I see this as a short term solution and not much more). I'm expecting it will be late next spring before I'm finished anyway.

The 110' distance is from meter to where I expect the service to enter the building. Guessing 125' of service cable will handle it.

However since I'm starting with nothing but $60 and a dream here, I can always move the location closer to the house by 6 - 8ft if it would help anything.
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I think 60A is more than a little optimistic, in this case. Sure, he MIGHT "get away with it"; but that should not be the criteria for designing a new service installation.
Mill, drill press, lathe, 3.5 HP compressor, 5kW heater, welder, two AC units, 42" TV, golf cart charger, etc, etc, 960 sq/ft - 2-2-2-4 AL MHF, 115' run, 70A breaker, no issues.
This is the truth and closer to the reality. 25 years ago I wired maybe a couple dozen garages and used 60A breakers, a couple of them maniacs worked in daily for all those years, never,,, not once, ever had a tripped breaker call.
 

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757
I'm in Huntsville AL. We have the benefit of relatively short, not-that-cold winters, but summertime heat indexes here can be brutal.

Even so, at least according to WikiPedia, you can reasonably expect freezing temperatures, at least overnight, from December through February. Given that, there would still be value in keeping that space minimally heated 24/7 through those months (maybe late November through early March). Think about all the paints and other materials you will presumably store in there, which don't take kindly to sub-freezing temperatures, even "occasionally".

A cool concrete floor is kind of nice in July or August.

No doubt!

Hmmm... I wonder if anyone has tried chilling the water in an in-floor hydronic system. That might be just the ticket for KEEPING those floors cool in the Summer. Probably not the most efficient way to cool the entire space, tho'.

For the near term I'm thinking a couple 48" or 60" ceiling fans.

I suppose for cooling there's just no getting around blowing air around, in SOME fashion. But the more you can keep the air velocity down, the less problems you're likely to have with airborne dust getting into your paint jobs and similar.

Also have a 3 burner propane heater (keep in mind I see this as a short term solution and not much more). I'm expecting it will be late next spring before I'm finished anyway.

Understood. But the key thing is to keep your options open when you do the initial steps of construction. Too many folks take something of a "penny-wise & pound-foolish" approach to such boring & mundane parts of the project as slabs, footers, etc.; and things like insulation get treated as an afterthought. By then, it's too late to do what would really be BEST.

Even in your climate, I am convinced that a well-insulated slab will be worth its weight in gold in the long run (well, maybe not gold; but certainly beer ;) ).

The 110' distance is from meter to where I expect the service to enter the building. Guessing 125' of service cable will handle it.

In which case, I suspect you'll be OK with AL 2-2-2-4 MHF.

However since I'm starting with nothing but $60 and a dream here, I can always move the location closer to the house by 6 - 8ft if it would help anything.

It can't hurt. As it stands, it's something of an "edge case" -- you'll very probably be just fine; but giving yourself a bit of "fudge factor" can only help.

 

Autorotica

Well-known member
Joined
Oct 21, 2012
Messages
526
Location
SE Pa
Hmmm... I wonder if anyone has tried chilling the water in an in-floor hydronic system. That might be just the ticket for KEEPING those floors cool in the Summer. Probably not the most efficient way to cool the entire space, tho'.



Cooling a floor with a radiant heat system has been attempted and unfortunately it has produced less than desirable results. Know what happens when hot air hits cool surface? The skin temp of the floor isnt cool enough to form liquid condensation, it just concentrates humidity like a machine built to do so.

Care for a little rain in your building?
Chris
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
This is the truth and closer to the reality. 25 years ago I wired maybe a couple dozen garages and used 60A breakers, a couple of them maniacs worked in daily for all those years, never,,, not once, ever had a tripped breaker call.

Got your back dude. :lol: I had all the same sh..stuff in my old 24x24 - less one AC unit - on a 60A. Never tripped it. One day I turned on all 14 T8 fixtures, the DP, lathe, mill, bench grinder (1/2 metric HP), ceiling fan, tripped the compressor and cranked the heater. It was too cold to run the 12K BTU AC unit. I clamped on one of the power legs and that side was drawing 49.1A.
 

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757
Cooling a floor with a radiant heat system has been attempted and unfortunately it has produced less than desirable results. Know what happens when hot air hits cool surface?

Boy Howdy, do I ever!

Back around the end of July, the top 30 feet or so of a 100+ foot tree near the edge of my property broke off during a severe thunderstorm The wind carried it across the yard, and it landed on my roof. Or rather, it landed IN my roof. The resulting several-foot gash then let in the driving rain in copious quantities. That in turn soaked the loose cellulose insulation to the point that my Dining Room ceiling could no longer support the weight; and about a half-hour later a section roughly 4'x4' landed on the floor. amid a large pile of soaking wet insulation. (Thank Ghod it wasn't the section from which the chandelier hung.) Fun stuff. :yikes:

We put a tarp over the hole in the roof as a temporary stop-gap measure, while I arranged for repairs. But over the next few weeks, with the weather still quite warm, the hot attic air would pour down through that gaping hole in the ceiling, hit the walls of the air-conditioned space below, and start small local rain showers -- it was LITERALLY dripping steadily over the archway into the Living Room, for example. By the time were were able to get things fixed (which, of course, took much longer than it should have, for all sorts of reasons), the top two feet or so of the walls were an entirely different color as a result of the incessant "steam cleaning". The previously unnoticed dirt & atmospheric crud that had been slowly building up over more than a decade since that room was last painted was now starkly obvious in big dark streaks leading down from that "cleaned" area at the top.

Oh, well. My wife wanted to re-decorate anyway. :rolleyes2

 
Last edited:
To avoid these ads, REGISTER NOW!
Top Bottom