Some very basic questions about Mr. Cool install

tahard00y

New member
Joined
Apr 22, 2026
Messages
2
This is a 24K unit, 5th gen going in a metal shop building. Looks like I will need to buy a 30amp fused breaker with cord separately. Does this mean that I need a 30amp breaker in my sub panel, or just a 20amp? Also, is the wire from the sub panel to the outside box supposed to be 10-2 wire or 12-2? The directions are confusing for a DIY person.
Thank you for any help and advice.
 
To avoid these ads, REGISTER NOW!

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,917
Location
Austin, TX
HVAC needs a physical disconnect outside nearby and MAY require an 120V accessory outlet. I'll let someone else speak on fuse/breaker/disconnect.

Follow the wire and fuse/breaker directions in the Mr. Cool manual. They are notoriously overwired from what I've seen, but that can't hurt.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,909
This is a 24K unit, 5th gen going in a metal shop building. Looks like I will need to buy a 30amp fused breaker with cord separately. Does this mean that I need a 30amp breaker in my sub panel, or just a 20amp? Also, is the wire from the sub panel to the outside box supposed to be 10-2 wire or 12-2? The directions are confusing for a DIY person.
Thank you for any help and advice.
You need a suitable breaker in the panel, feeding a disconnect at the outside unit. The disconnect may or may not need to be fused, depending on what the name plate on your unit says. (The name plate, not what the manual says, not what someone tells you in email or on the phone , but the name plate on your unit, not someone else’s. Specs change faster than documentation, and the nameplate is controlling.). If it says “max fuse“, then you need a fused disconnect. And “fuse” means fuse, not a breaker, a fuse. If it says “max overcurrent protection “, than you can use a disconnect without a fuse, as long as the breaker is sized properly. If you don’t have your machine yet, I would install a fused disconnect. There’s not much downside to having one when you don’t need it, the fuses will never blow unless there is a fault.

Additionally, you need a 120v receptacle within 25 feet, at the same level. That’s for servicing and installation.
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,453
Location
VT
Follow the wire and fuse/breaker directions in the Mr. Cool manual. They are notoriously overwired from what I've seen, but that can't hurt.

Incorrect

Follow the fuse/breaker requirements on the equipment label.

The manuals have been wrong on these units. In my case manual called for a breaker, but when the unit arrived the tag clearly required a fuse.

It may be semantics to some, but as I learned its code.
 

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,312
Location
Texas
I’ve run across recommendations for a surge suppressor at the unit site to protect the control board.
 
OP
T

tahard00y

New member
Joined
Apr 22, 2026
Messages
2
Thank you all for this help! I can definitely put an outlet on the wall nearby.