I need a 25' run from Honda eu7000is to power inlet on power pole. 8ga 4 wire needed. Is the wireandcableyourway soow cable suitable for this.?
 
To avoid these ads, REGISTER NOW!
OP
R

Raisedonadeere

Well-known member
Joined
Jul 31, 2017
Messages
436
Location
Central KY
Thanks, it is temporary power outage kind of thing but might be left outdoors quite a bit. So I would like to know that it will stand up to outside conditions like powering a RV that is being lived in for a few months and the like. Is there a better choice? I am not familiar with the various cable types. Got into is a bit when installing some Minisplits but that is it. Bought some welding cable once but just on someone else's say so, didn't actually know what I had.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,409
Location
VT
Conduit and thwn

This.

Leaving soow laying around screams hack. Run the conduit to the inlet, then use a short cable to connect the generator when you put it outside.

Or put the insect on the side of the garage and get a 25' generator cord.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,651
Location
Long Island
Thanks, it is temporary power outage kind of thing but might be left outdoors quite a bit. So I would like to know that it will stand up to outside conditions like powering a RV that is being lived in for a few months and the like. Is there a better choice? I am not familiar with the various cable types. Got into is a bit when installing some Minisplits but that is it. Bought some welding cable once but just on someone else's say so, didn't actually know what I had.
Honda makes great generators, and for occasional use, I see no issues. But keep the oil change interval in mind. Honda recommends oil changes at the first 20 hours, and every 50 hours thereafter. It's a splash lubricated machine (no filter), so it isn't built for true continuous use.
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,997
Location
Central Iowa
I'd use cord and not give it a second thought other than when mowing. If it's available in 8/4 I would probably get SJOOW instead and have less of a fight getting it to fit the cord caps.
 

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
I'm not sure 8ga wire is needed for a generator that is rated for 5500 watts continuous. (according to specs found on-line for eu7000is) 5500 watts, at 240 volts, is 22.9 amps.... It seems to me you can easily get bey with 10ga wire, which is rated for 30 amps.

Most power "inlet boxes" are either rated for 30, or 50 amps.... 8ga wire is rated for 40 amps.... To me, 8ga wire would be over sizing a cord for 30 amp service, or under sizing a cord for 50 amps service.

Of course total length is a factor when considering voltage drop but at 25 feet (as OP mentioned) I doubt that is an issue.

This is just me thinking out loud.... don't take my word as fact for anything.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,860
Location
Richmond, VA
I'm not sure 8ga wire is needed for a generator that is rated for 5500 watts continuous. (according to specs found on-line for eu7000is) 5500 watts, at 240 volts, is 22.9 amps.... It seems to me you can easily get bey with 10ga wire, which is rated for 30 amps.

Most power "inlet boxes" are either rated for 30, or 50 amps.... 8ga wire is rated for 40 amps.... To me, 8ga wire would be over sizing a cord for 30 amp service, or under sizing a cord for 50 amps service.

Of course total length is a factor when considering voltage drop but at 25 feet (as OP mentioned) I doubt that is an issue.

This is just me thinking out loud.... don't take my word as fact for anything.
10/4 is common with generator cords, but it's actually only rated for 25a. That said, think 10/4 would be fine as well, but upsizing won't hurt other than weight and in the wallet
 

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
10/4 is common with generator cords, but it's actually only rated for 25a. That said, think 10/4 would be fine as well, but upsizing won't hurt other than weight and in the wallet
Yep, I have several 10/4 generator cords and my generator is larger than the one mentioned in post #1.

I agree, up sizing does not hurt.... but OP originally said 8ga wire was "needed"..... my post above was just me trying to tell him that 8ga is probably not "needed".

However, 8ga wire can certainly be "wanted". lol
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,592
Location
Fullerton, CA
Most power "inlet boxes" are either rated for 30, or 50 amps.... 8ga wire is rated for 40 amps.... To me, 8ga wire would be over sizing a cord for 30 amp service, or under sizing a cord for 50 amps service.
There is no such thing as a 40A receptacle, plug, or inlet. A 50A is proper and Code approved.
 

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
There is no such thing as a 40A receptacle, plug, or inlet.

That's exactly what I was trying to say when I said: "To me, 8ga wire would be over sizing a cord for 30 amp service, or under sizing a cord for 50 amps service"

You said it much better than I did.

A 50A is proper and Code approved.

Correct, and so is a 30A inlet.

I don't think a 50 amp inlet is necessary for 22.9 amps of continuous power. That is all....

He can buy whatever he wants to buy.... I don't care. lolol
 