Speedaire compressor problem

mcas

Member
Joined
May 5, 2024
Messages
9
I have.a 80gl speedaire 1wd71…. compressor cut in and cut out off his limits ..145 -175…..and run and stop in a seconds frequently…i change the pressure switch and the check valve and the same problem continues….when i start the compressor after i replace both parts just cut off until 100 psi…then start again in a few and cut out…dont go over 150 …off cycles
 
To avoid these ads, REGISTER NOW!

MacMcMacmac

Well-known member
Joined
Oct 21, 2014
Messages
1,614
Location
canada
I am having some trouble following you, but it sounds a bit like the pressure switch might be plumbed in before the check valve. A picture would be very helpful.
 

Jswain

Well-known member
Joined
Apr 26, 2013
Messages
2,467
Location
Calgary, AB
A picture of the pressure switch for sure. Did you buy a 30psi differential 145-175?

They come in all ranges, you could have bought one set for 150psi.
 
OP
M

mcas

Member
Joined
May 5, 2024
Messages
9
Hi ..thanks for your reply..i attach some pics
 

Attachments

  • IMG_1106.jpeg
    IMG_1106.jpeg
    871.7 KB · Views: 36
  • IMG_1105.jpeg
    IMG_1105.jpeg
    642.2 KB · Views: 34
  • IMG_1104.jpeg
    IMG_1104.jpeg
    1 MB · Views: 33
OP
M

mcas

Member
Joined
May 5, 2024
Messages
9
Every 3 seconds start and stop
 

Attachments

  • image.jpg
    image.jpg
    631.9 KB · Views: 30
OP
M

mcas

Member
Joined
May 5, 2024
Messages
9
yes start and shut off again…i check the pressure switch power i think its the contactor cuz when its between the 140 and 175 the switch its sending the power to closed the coil in the contactor and its on for 3 sec and off ….could be ?….how can i make sure its the contactor
When it turns off do you have to hit the blue reset button to start it again?
 

Attachments

  • IMG_1108.jpeg
    IMG_1108.jpeg
    659.9 KB · Views: 24
  • IMG_1109.jpeg
    IMG_1109.jpeg
    831.5 KB · Views: 29

Jswain

Well-known member
Joined
Apr 26, 2013
Messages
2,467
Location
Calgary, AB
If you need to hit the blue reset button to make it restart, it is likely a problem with the electric motor/wiring making it draw too many amps, or the contactors trip needs to be set higher.

What voltage do you have it wired for, 230v or 460v?
 
OP
M

mcas

Member
Joined
May 5, 2024
Messages
9
230v….but when i test the in line power in the contactor. Read 280
 
To avoid these ads, REGISTER NOW!
OP
M

mcas

Member
Joined
May 5, 2024
Messages
9
280v between l1.l2 and l3 in the safety switch
its a delta configuration…when i test to ground each pole.. 1 of them no reading… im correct?
 
OP
M

mcas

Member
Joined
May 5, 2024
Messages
9
If you need to hit the blue reset button to make it restart, it is likely a problem with the electric motor/wiring making it draw too many amps, or the contactors trip needs to be set higher.

What voltage do you have it wired for, 230v or 460v?
Start and shuts off every 3 seconds until reach 175 psi thats the cut off set up
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,451
Location
Beautiful Southern Maryland
I think you need to go back to basics and all the way back to the panel or nearest shut off. I am not that familiar with 3 Phase Delta but there are others here that will tell you what you should read. For some reason the 280v you got on one test did not sound right to me but I could very well be wrong there.
 

RPH

Well-known member
Joined
Dec 17, 2006
Messages
4,190
Location
Michigan Thumb
How are the overloads programmed? The blue switches set up the amp set point and the other I can’t tell. But I guess it’s a timing aspect when to trip. Get the instructions for the contactor/overload unit. Start there.
 
OP
M

mcas

Member
Joined
May 5, 2024
Messages
9
How are the overloads programmed? The blue switches set up the amp set point and the other I can’t tell. But I guess it’s a timing aspect when to trip. Get the instructions for the contactor/overload unit. Start there.
Thanks ..i will check that
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
2,021
Location
East Cobb County, Georgia
280v between l1.l2 and l3 in the safety switch
its a delta configuration…when i test to ground each pole.. 1 of them no reading… im correct?
Except for the voltage, that sounds like you have service from a corner grounded delta transformer. Could you confirm for us what your service is, and how you get 120V/1PH (if at all)? And, are you sure you are seeing 280V across all three line to line pairs? You may have a transformer issue (yours or the PoCos) leading to over-voltage.
 

KenC

Well-known member
Joined
Dec 20, 2009
Messages
2,609
Location
oklahoma
Except for the voltage, that sounds like you have service from a corner grounded delta transformer. Could you confirm for us what your service is, and how you get 120V/1PH (if at all)? And, are you sure you are seeing 280V across all three line to line pairs? You may have a transformer issue (yours or the PoCos) leading to over-voltage.
Line to line voltage readings as well as line to ground will help a lot. 280 is really strange, I'd expect 208 in some buildings, or in my case it would be 218ish on the high leg and 120something on the others.
 