Splicing different gauge wire

check251

Well-known member
Joined
Oct 15, 2010
Messages
78
Location
PA
I have 60' of 1 1/2" schedule 40 pvc buried to my garage. I plan to feed it with 2 gauge MHF. I will use 75' SER indoors from my main panel to a splice box. My question is can I use 2-2-4-6 MHF which will be a little easier to pull through the conduit and spliced to 2-2-2-4 SER inside? I can't seem to find 2-2-4-6 SER. This will be protected with a 90 amp breaker, total run will be close to 150'.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,016
Location
Modesto, CA
What kind of loads will u have in the garage?

2-2-4-6 has a reduced neutral. If u have a lot of 240v loads and minimal 120v loads u should be good.
 
OP
C

check251

Well-known member
Joined
Oct 15, 2010
Messages
78
Location
PA
Thanks for the reply Wylie. I have a compressor that is currently wired to 120 but can be 240v. Maybe someday a lift or welder. It's 24x36 that is mostly used for storage currently. I have some woodworking tools that are all 120v in my basement that might get moved there.
 
To avoid these ads, REGISTER NOW!
OP
C

check251

Well-known member
Joined
Oct 15, 2010
Messages
78
Location
PA
Thanks Pattenp, I pulled 2 gauge copper a few months ago about the same distant and amount of turns. These were individual wires, I don't recall if the ground was reduced and we had trouble pulling.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,016
Location
Modesto, CA
Thanks Pattenp, I pulled 2 gauge copper a few months ago about the same distant and amount of turns. These were individual wires, I don't recall if the ground was reduced and we had trouble pulling.

The EGC aka grounding conductor aka ground wire will always be smaller than the ungrounded or grounded conductors.
 
OP
C

check251

Well-known member
Joined
Oct 15, 2010
Messages
78
Location
PA
No we didn't. Several times I said "Scott, you know they make lube for this." I have a bottle for mine. No wire yet, but a bottle of lube I have.
 