billrigsby

Well-known member
Joined
Mar 17, 2017
Messages
58
I am doing a lot of re-wiring after a small room removal.
Currently I have several groups of wires from the ceiling and
several from the now non-existent walls. I am going to re-route
all of this spaghetti through cabinets, up and down the wall to
new switches etc.

Needless to say, most if not all of these existing wires are too short.
Question;

Is there an acceptable way to splice wires without doing the accessable
box and cover route? I am not concerned with code, just want to have
this done without five or six boxes and blanking plates in the ceiling
and wall.

Is there anything really wrong with soldering and heat-shrinking, (maybe
double up on the heat-shrinking) the wires?

Where I can (inside of cabinets I will go the box route), but the others?
not so much. I am open to boxes without covers and buried (for ever).?


Comments and Opinions?



Bill
 
Last edited:
To avoid these ads, REGISTER NOW!

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,850
Location
Niagara Region, Ontario, Canada
by no means an electrician here, but knowing that many fires are caused by electrical , and you knowing there is a code in place, (and for obvious reasons), why do you ask such questions...
 
Joined
Jul 24, 2016
Messages
3,371
Well if this were in a garage I might not, but this is in a living room,
is it at all acceptable to splice in a box, but not have the box accessible?


Bill

Not by code. This matters because if you ever sell the place, then you have to disclose it, or it can come back on you. What amount of wires are we talking about, and how far away to other boxes that ARE staying or the electrical panel, for replacing the wires?
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,591
Location
Long Island
Well if this were in a garage I might not, but this is in a living room,
is it at all acceptable to splice in a box, but not have the box accessible?

Bill

No, but you're asking the wrong question...

Not by code. This matters because if you ever sell the place, then you have to disclose it, or it can come back on you. What amount of wires are we talking about, and how far away to other boxes that ARE staying or the electrical panel, for replacing the wires?

This for example:
https://www.homedepot.com/p/Tyco-Electronics-Romex-Splice-Kit-2-Wire-1-Clam-A22899-000/202204326

is UL Listed to splice two Romex (NM) 12-2 or 14-2 cables and be hidden in a wall. So, with a Listed splice kit, there are options to bury a splice. But there are no options to bury a box.

Now the splice kit in the link above has one cable in, and one cable out. If you need a T connection, then there are other kits for that.
 

gicts

Active member
Joined
Jul 7, 2014
Messages
33
Location
Louisville
An option could be to put junction boxes on the wall of the cabinets (and of course still have them accessible).
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,121
Location
SE MI
YES, you can do a NM-B wire splice buried in a wall !
• NEC compliant (Article 334-40b, 2005 and 2008)
• UL and CSA listed
Capture.JPG

Tyco Electronics Romex Splice Kit, 2 Wire (plus ground)

They have versions for 3 wire AND a tap !

This saved my bacon on a recent kitchen remodel. Previous owner had butchered the wiring and had splices with wire nuts buried. These fixed everything.
 
Last edited:

Lassen Forge

Well-known member
Joined
Apr 26, 2014
Messages
15,097
Location
The romantic hills of central Umbria, Italy,
NEVER bury a junction box in the wall.

Because when you want or need to go back into it you need to rip up a wall to find it and fix it, and when you or a subsequent property owner dries a nail through it and shorts themselves out...

Yeah Just don't. Please. They make decorative covers for this...

Me? I'd just run new wire. When you look at the consequence of this junction corroding in 50 years and getting hot, well... just not worth it.
 
To avoid these ads, REGISTER NOW!
OP
B

billrigsby

Well-known member
Joined
Mar 17, 2017
Messages
58
Accessible attic above?

Unfortunately - NO


An option could be to put junction boxes on the wall of the cabinets (and of course still have them accessible).

That I am going to do, it is the ceiling wires that will be too short.

NEVER bury a junction box in the wall.

Got it!

Just do it right, go back to the last j-box and replace the wire with wire the correct size and be done.

I thought about that, worst thing that could happen when re-pulling
wire through the ceiling is loosing my pull cable and then having to
opening up the sheet rock.


No, but you're asking the wrong question...

This for example:
https://www.homedepot.com/p/Tyco-Electronics-Romex-Splice-Kit-2-Wire-1-Clam-A22899-000/202204326

is UL Listed to splice two Romex (NM) 12-2 or 14-2 cables and be hidden in a wall. So, with a Listed splice kit, there are options to bury a splice. But there are no options to bury a box.

Now the splice kit in the link above has one cable in, and one cable out. If you need a T connection, then there are other kits for that.


YES, you can do a NM-B wire splice buried in a wall !
• NEC compliant (Article 334-40b, 2005 and 2008)
• UL and CSA listed
Capture.JPG

Tyco Electronics Romex Splice Kit, 2 Wire (plus ground)

They have versions for 3 wire AND a tap !

This saved my bacon on a recent kitchen remodel. Previous owner had butchered the wiring and had splices with wire nuts buried. These fixed everything.

This seems like the route to go,
Food for thought and grounds for further research
:thumbup:
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,714
Location
NW Iowa
YES, you can do a NM-B wire splice buried in a wall !
• NEC compliant (Article 334-40b, 2005 and 2008)
• UL and CSA listed
Capture.JPG

Tyco Electronics Romex Splice Kit, 2 Wire (plus ground)

They have versions for 3 wire AND a tap !

This saved my bacon on a recent kitchen remodel. Previous owner had butchered the wiring and had splices with wire nuts buried. These fixed everything.

Unless this is better than the versions I've seen then I would never be caught using one. Legal yes, but it reminded me of the push in connectors on outlets. Not something I would want to be inaccessible in a wall.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Unless this is better than the versions I've seen then I would never be caught using one. Legal yes, but it reminded me of the push in connectors on outlets. Not something I would want to be inaccessible in a wall.

unlike backstabbed outlets, Ive never heard of or seen one fail so im not gonna dog them. Convince me otherwise
 
Joined
Jul 24, 2016
Messages
3,371
YES, you can do a NM-B wire splice buried in a wall !
• NEC compliant (Article 334-40b, 2005 and 2008)
• UL and CSA listed
Capture.JPG

Tyco Electronics Romex Splice Kit, 2 Wire (plus ground)

They have versions for 3 wire AND a tap !

This saved my bacon on a recent kitchen remodel. Previous owner had butchered the wiring and had splices with wire nuts buried. These fixed everything.

They use them in mobile homes, but I'd be leery.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,121
Location
SE MI
unlike backstabbed outlets, Ive never heard of or seen one fail so im not gonna dog them. Convince me otherwise

From what I read, these were approved for modular homes awhile back (10-20 years ?). They proved their reliability and got brought in for general (probably non commercial only) use. Kind of like Mobil Home Feeder (MHF) cable. Proved in the field, now general usage (within limits).
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
They use them in mobile homes, but I'd be leery.

I would rather have any splices accessible, just out of my comfort zone to bury them in a wall.

Mobile homes are absolutely the bottom of the line when it comes to dwellings, built as cheap as they can get away with. You can fill them with upgraded appliances, nicer finishes, but underneath they still cheap, to paraphrase others, like putting lipstick on a pig.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,052
Location
Minneapolis
I've heard of those in-wall splices but have never seen one in person. Depending on where you live I've heard they may not be allowed by local codes, so it would best to check first.
 

Crazyjake8493

Well-known member
Joined
Sep 26, 2014
Messages
3,952
Location
Upstate NY
They use them in mobile homes, but I'd be leery.

They use them often in RV’s as well for the 120V AC wiring, I replaced at least a few that had poor connections.

UL listed, sure. I wouldnt be caught using one, and I wouldn’t recommend one unless they were willing to open up the wall at some point if it fails. I know my wire nut or Wago splices in a box won’t fail for no reason.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Seems like a good idea as long as they are not just friction fit -- do they use screws (like a back wire outlet) or a pressure lever like those new things ?

I have found some scary stuff buried in walls throughout the years
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,591
Location
Long Island
Seems like a good idea as long as they are not just friction fit -- do they use screws (like a back wire outlet) or a pressure lever like those new things ?

I have found some scary stuff buried in walls throughout the years

If you're talking about the Tyco splice kit, the electrical connection to the wire is an insulation piercing fork. Each half pinches the wires under the insulation much like a 66 block does, with a plastic retention piece that holds the wire in the fork. It's kind of like a Scotchlok, but much beefier. This clicks closed in several places, and eventually screws help hold it closed.

A plastic clamp pinches the jacket, and the metal E holds the cable to prevent it from being pulled out. Then, each half clicks into the other half to make the connection.

I just did a few. If I have any more to do in the near future, I'll try to remember take some pics.

I trust them a little more than a Scotchlok. My feeling is that if it fails (a not unlikely proposition), it will at least fail safe (open) and not fail short. So, it won't burn your house down, but you may end up having to cut holes to fix down the road.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,714
Location
NW Iowa
I wonder if someone make something similar to a UF splice that could be buried in a wall. That I might be comfortable with. A UF splice has brass terminals with setscrews that make a solid connection.
 

jdieter

Well-known member
Joined
Nov 17, 2007
Messages
320
Location
Northern Indiana
No local code so I used UF splice kits in my remodel. Couldn't justify the expense of tearing apart a vaulted ceiling. Another option that I've used on switch legs are wireless switches, but the hot wire has to be present in the box with the fixture.
 