Split bolt or Wire Nuts 10/2

AllDodge

Well-known member
Joined
Feb 18, 2015
Messages
130
Location
KY
Dryer wiring 10/2 W ground
Older wiring where the ground is copper braid around the 2 conductors, and appear to be tinned copper, rubber jacket not vinyl.

Hot wires are a tad to short in the breaker box, ground braid is plenty long. I'm thinking of using split bolt connectors inside the breaker box to make them longer to reach the breaker location. Could use wire nuts but I like split bolt and tape because there tighter IMO.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
umm, :wtf: a 3-wire dryer circuit should be 10/3 NM W/O grnd. meaning 2 hots & an insulated neutral.

what you have is NOT kosher since the neutral conductor is NOT insulated. good way to shock someone.... :shocking:

This circuit should be ripped out & replaced w/ 10/3 NM-b w/ grnd....

NEVER use a bare wire for a neutral/grounded conductor.... :shocking:

and what you have sounds like 10/2 SEU NOT NM since the ground is braided...
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,709
Location
NW Iowa
umm, :wtf: a 3-wire dryer circuit should be 10/3 NM W/O grnd. meaning 2 hots & an insulated neutral.

what you have is NOT kosher since the neutral conductor is NOT insulated. good way to shock someone.... :shocking:

This circuit should be ripped out & replaced w/ 10/3 NM-b w/ grnd....

NEVER use a bare wire for a neutral/grounded conductor.... :shocking:

and what you have sounds like 10/2 SEU NOT NM since the ground is braided...
SE was definitely legal...

While you can't extend the circuit I see no issue adding a bit of wire in the panel. It's pretty common when you're changing a panel.
 
OP
A

AllDodge

Well-known member
Joined
Feb 18, 2015
Messages
130
Location
KY
Home built in 1969 and panel replaced from Federal Pacific (fire starter panels) to Square D about 12 years ago. I installed a 80 Kva surge suppressor (2 days ago) and breaker was marked as not used (even though it was ON). So when wife couldn't turn dryer ON I need to fix.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
SE was definitely legal...

While you can't extend the circuit I see no issue adding a bit of wire in the panel. It's pretty common when you're changing a panel.
SE with an UNINSULATED neutral for a 3-wire dryer circuit? i dont think so.
 
OP
A

AllDodge

Well-known member
Joined
Feb 18, 2015
Messages
130
Location
KY
SE with an UNINSULATED neutral for a 3-wire dryer circuit? i dont think so.
There is a jacket around the braid and wires, so its not in the open
Same thing which was on my older house at the service head. Replaced that also when rewired the whole hose from 80 amp to 200 amp
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,709
Location
NW Iowa
SE with an UNINSULATED neutral for a 3-wire dryer circuit? i dont think so.
I DO think so and 250.140 exception (3) agrees with me.

Se has always had an uninsulated neutral. It was the standard for range circuits and sometimes dryer circuits for many, many years.
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
SE with an UNINSULATED neutral for a 3-wire dryer circuit? i dont think so.
As long as it originated in the main panel, it was permitted, never cared for it being done that way, but it would not be 10 AWG either, if it is 10/2 NM it was never code compliant & must be removed.
 
To avoid these ads, REGISTER NOW!
OP
A

AllDodge

Well-known member
Joined
Feb 18, 2015
Messages
130
Location
KY
The old wire looks tinned plated copper. Guess no need to worry about corrosion
 

Two Sheds

Well-known member
Joined
Jan 16, 2014
Messages
101
A lot of SE cable was aluminum. Be double sure it's copper before using wire nuts. If it is aluminum you need splices rated for aluminum and no-corrode paste.
 
OP
A

AllDodge

Well-known member
Joined
Feb 18, 2015
Messages
130
Location
KY
More info as to reason for the question:
Need to reconnect dryer, and dryer should be on a 30 amp breaker with 10 AWG wire.
I'm looking at the wire thinking that's big for 10 but haven't wired anything in a long time

Also noticed dryer breaker was a 40 amp

OK get some of Dad's (retired local 369 and passed away many years ago) split bolt and smallest he had was ones that would barely fit the wire. Had 1/2 nut and 3/8 split

Dad also saved wire and I still have most of it and found wire that was same size and used it.

All finished and now do believe it was 8 or 6 AWG. Got the caliper out (just now) and its 7 strand and 0.16 diameter. So this is #6 and also a reason just getting the wire in the 30 amp took a bit more work

Edit decimal in wrong place
 