To avoid these ads, REGISTER NOW!

Split Wired GFCI

FlavortownPublicWorks

Active member
Joined
Jun 27, 2018
Messages
29
Location
SE Michigan
Couldn't find this in a search, though I'm sure it's been covered.
Seeing that GFCI outlets can't be split wired (different circuits for top and bottom outlets in a box), how do I add GFCI protection to split wired circuits? Are GFCI breakers the only way to do this?
 
To avoid these ads, REGISTER NOW!

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
Are you looking for a split wired circuit that uses a single feed, and one is switched, or uses 2 different feeds?

If it's a single feed, I think a GFCI outlet upstream of where the wire splits would work.

If 2 different feeds, then you would need a 240V GFCI breaker I think. Unless they each use their own neutral, and then 2 separate 120V GFCI breakers would work. Or 2 GFCI outlets upstream of the outlets would also work.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
GFCI breaker or install a GFCI receptacle at each location are the only choices that I see.
 
To avoid these ads, REGISTER NOW!

shadycrew31

Well-known member
Joined
Jun 23, 2017
Messages
58
Location
Burbs of Philly
You might be able to use dead front GFCI's at the start of your loop. They are typically used applications where the outlet or item required to have GFCI protection is inaccessible.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,014
Location
Modesto, CA
Couldn't find this in a search, though I'm sure it's been covered.
Seeing that GFCI outlets can't be split wired (different circuits for top and bottom outlets in a box), how do I add GFCI protection to split wired circuits? Are GFCI breakers the only way to do this?

Are you talking about a multi-wire branch circuit(shared neutral) that feeds one receptacle with the 2 outlets getting separate hot legs?

Only way to have GFCI protection for that is with a double pole GFCI breaker...
 

pjmariner

Well-known member
Joined
Jun 15, 2018
Messages
71
Location
Marshfield MA
GFCI doube pole breaker is how I am doing it. I am going to do a writeup soon in my garage thread. I ran 12/3(with ground romex) . The breaker for my panel was $90, but not needing any GFI outlets, the contractor packs of standard outlets cost next to nothing.

I am doing surface mounted 4 square boxes with 2 duplex outlets per box, 1 white outlet for 1 circuit, 1 almond outlet the other. The goal is being able to run a vacuum and tool at same box on different circuit on all my boxes

Also, if you are doing multi-wire branch circuit you have to pigtail your connections, you cant use the outlets alone to continue the circuit.
 

Lonnies Performance

Well-known member
Joined
Aug 20, 2017
Messages
267
Location
Pittsburgh, PA
GFCI doube pole breaker is how I am doing it. I am going to do a writeup soon in my garage thread. I ran 12/3(with ground romex) . The breaker for my panel was $90, but not needing any GFI outlets, the contractor packs of standard outlets cost next to nothing.

I am doing surface mounted 4 square boxes with 2 duplex outlets per box, 1 white outlet for 1 circuit, 1 almond outlet the other. The goal is being able to run a vacuum and tool at same box on different circuit on all my boxes

Also, if you are doing multi-wire branch circuit you have to pigtail your connections, you cant use the outlets alone to continue the circuit.

I did the same thing.... a 20A 2 pole 240V GFCI breaker feeding a quad receptacles.
Works well, no nuisance trips & it also gives more available power at any 1 location when you plug multiple devices into adjacent outlets.
 