Splitting service to barn

Cb-man

Well-known member
Joined
Jul 19, 2013
Messages
165
Location
Newport, MI
Hello there.
In the midst of all my projects i am running power to my barn.
I am installing a 100 amp panel in the barn.
My friend is an electrician and lineman. Works for DTE the local power company.

My question is how can i split the service after or at the meter?
He suggested stuffing both wires in the lug in the meter.
Its an old milbank meter socket.
I know the sell double lugs but dont know if it will attach in my meter.

Are there any other ways to split? Like a junction box or inside the 100 disconnect/breaker i have to put on the house before the barn?
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Well the one thing you shouldn't do is put two wires in one lug. If your outside disconnect panel has space for a second breaker then add one for the barn. If the house panel has open spaces you can add a breaker for the barn and go from the house panel. A picture of the existing disconnect panel opened up would help with answering your questions.
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
Probably isn't an outside disconnect in Edison land. What size service do you have coming in from edison? Overhead or underground?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
Does your meter pan have dual lugs?

As pattenp said, post up some pics so we can see what u have!
 
Last edited:
OP
C

Cb-man

Well-known member
Joined
Jul 19, 2013
Messages
165
Location
Newport, MI
I have 320 amp overhead service. The meter can is an old 1975 milbank from when the house was built. I do not believe it is dual lug.
Im not fond of double tapping it.
Maybe i should replace the can. But im pretty sure getting the conduit out from the over head will be a pain.
Is there some disconnect or panel or junction i could run to straight out of the meter? Then split it?
A link to the right part would help.
I only boughy enough wire for 3 runs but i guess i could go buy a 4th for a ground and just run it in my house panel.
But im not sure the wire i bought for the run would reach to my panel
 
OP
C

Cb-man

Well-known member
Joined
Jul 19, 2013
Messages
165
Location
Newport, MI
Also the disconnect i bought is just a 100 amp outdoor breaker. Two hot in two hot out and neutral
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
Well you have to pull 4 wires no matter what if your putting a dc up by the meter.
Also I do not think edison ever issued a 320 overhead. So definitely need to see a picture of this setup.
How large is the house? How large is your main plane in the house?
 
To avoid these ads, REGISTER NOW!
OP
C

Cb-man

Well-known member
Joined
Jul 19, 2013
Messages
165
Location
Newport, MI
I will have to get up there for a pic.
The house is 1700 sq ft. I called edison and they told me 320.
The house did have a push matic 100 amp panel in it.
Even my friend who works there said its fine.
Im running a 200 amp panel in the house but replaced the main with 100 amp.

Why would i need to run 4 wires unless it was coming out of the main panel?

If its a seperate feed from the meters its a seperate service like the house. Two hots one neutral and the panel is grounded
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
Post up PIC's so the GJ Sparky's can help you out.

Don't think you're "electrician" friend is giving good advice . . . if his suggestion was to double up wires at the meter !! :scared:

Pictures of meter, meter enclosure, main house panel (cover ON . . and cover OFF).

What is DISTANCE from the house/meter to detached barn ???

:needpics:
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
I will have to get up there for a pic.
The house is 1700 sq ft. I called edison and they told me 320.
The house did have a push matic 100 amp panel in it.
Even my friend who works there said its fine.
Im running a 200 amp panel in the house but replaced the main with 100 amp.

Why would i need to run 4 wires unless it was coming out of the main panel?

If its a seperate feed from the meters its a seperate service like the house. Two hots one neutral and the panel is grounded

u mentioned the possibility of using a disconnect after the meter. If u do that then u will need a 4-wire feeder- 2 hots neutral and EGC. U will also need grounding electrodes for the barn subpanel.
 
OP
C

Cb-man

Well-known member
Joined
Jul 19, 2013
Messages
165
Location
Newport, MI
Alright. Even if its not 320 service coming in i have a 100 amp breaker at the house and the barn will be 100 amps.

I have two people helping me. My friend that works at DTE to cut power and do the work.
Also i work at marathon oil. We have certified electricians. I went over the code book with him for size of wire and how many feeds.
Since the barn isnt fed from the main panel it is a seperate feed we found you only need 3 wires.

I believe my panel at the house is feed through so i may go that way. Seems easier than messing with the meter.
 

jekquist

Well-known member
Joined
Apr 6, 2016
Messages
65
Location
Pinckney, MI
Ke electric supply has the best price I have found for wire. They are off of school craft in Livonia. I am running 100A service to my barn as well.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
51,081
Location
Northern Central Ohio
If I had it to do over again, I would have bought one of these my my garage.




Once it's in, you should "never" have to call the PoCo to pull the meter, just flip the disconnecting main.
 