Spray foam or fire stop wire holes?

signcrafter

Well-known member
Joined
May 9, 2012
Messages
12,495
When you drill a hole from the 1st floor down to basement or 1st floor up into attic do run a wire(or plumbing pipe for that matter) do you put some spray foam in that hole or firestop foam? Is there a code that says this? Also what about where the wire goes into the plastic electrical boxes? Is there a code that says you have to do anything there or is it good practice to hit it with a dab of great stuff? Any other areas where you need to do anything for electrical(or plumbing)?
 
To avoid these ads, REGISTER NOW!

850xpeps

Well-known member
Joined
Aug 6, 2017
Messages
1,365
Acoustical sealant. The black tar is what I use. Stays flexible but seals the penetration. You can foam the remainder of the hole.

Into the basement doesn’t need anything.
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
There are code issues. You should check with your local AHJ to find out what they want to see in those holes. In our area, you have to use fireblock foam, not the generic expanding foam or any other goop that's not made for this application.
CD
 

850xpeps

Well-known member
Joined
Aug 6, 2017
Messages
1,365
There are code issues. You should check with your local AHJ to find out what they want to see in those holes. In our area, you have to use fireblock foam, not the generic expanding foam or any other goop that's not made for this application.
CD



As far as I’m aware fire stop is not required by code inside a residence. Only when an attached garage or multi family unit is involved.
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
As far as I’m aware fire stop is not required by code inside a residence. Only when an attached garage or multi family unit is involved.

Fireblock isn't firestop.
As I said, it depends on AHJ. If the OP is working under the rules of IBC or IRC then he may need to use something to be in compliance.
CD
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,971
Location
East Cobb County, Georgia
Most AHJs we work with accept fire block foam (the orange Great Stuff readily available), but one requires fire caulk (the red 3M stuff also readily available).
 

MoonRise

Well-known member
Joined
Nov 5, 2010
Messages
4,031
Location
NJ
Yes, even in residential construction or renovation nowadays you have to use the fireblock type caulk.

Inspector insisted on some remodel/addition work a while ago, even though the entire rest of the house had none. All the 'new' work penetrations had to have the 'rated' fireblock caulk.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
That's what fireblock does. Keeps air away from fires.
CD

No they're concerned about energy usage,not stopping fires.
You can drill 2" holes through every stud in a wall if you want as long as it doesnt affect energy efficiency standards by letting in non conditioned air .
I've been told the same story by many inspectors on many jobs when I asked them about fire caulking holes in walls.
 
To avoid these ads, REGISTER NOW!

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
I tried to burn the orange great stuff and it burns just as quickly as the regular great stuff. Just dyed orange and a couple bucks a can added.



Sent from my SM-G960U using Tapatalk
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
No they're concerned about energy usage,not stopping fires.
You can drill 2" holes through every stud in a wall if you want as long as it doesnt affect energy efficiency standards by letting in non conditioned air .
I've been told the same story by many inspectors on many jobs when I asked them about fire caulking holes in walls.

Yes, I realize this. My point was that fireblock uses the same theory. Keeping air from moving around.
CD
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
I tried to burn the orange great stuff and it burns just as quickly as the regular great stuff. Just dyed orange and a couple bucks a can added.



Sent from my SM-G960U using Tapatalk

It shouldn't be much different. It's not designed with any firestopping materials.
 

driftpin

Well-known member
Joined
Dec 22, 2016
Messages
11,304
Location
Miami-Dade/Broward Co. Florida
We had an in-service for the Broward County (Ft. Lauderdale FL area) county fire inspectors where a NFPA video was shown, where a test was done on wall penetrations. It was a sobering video, as it showed rapid expansion into the other side, of fire gases, which is usually what can kill you, not direct exposure to fire. The penetration was small, I don't recall the exact size, but I believe it was 1/8". The opposite room from the fire source became charged with carbon monoxide moving through the wall penetration, in a matter of minutes, making the room an asphyxiation chamber.

The AHJ is always whom you have to-satisfy. However, if you're protecting your loved ones, above-code is that-much-more protection. You may-not need to do it, but if the cost is minimal, why-not do it?

When I was a youngster, a family down the block had a late-evening house fire, single-family residences in a fairly-new construction area. The two boys were my age and 2 years-older, the older kid was asphyxiated and died. Our home was 5 or 6 years-old by then, and I don't recall the fire's origin, but it was the first time I had someone I knew who died. I don't think it had any cause for me to enter a career as a firefighter/paramedic and fire service instructor and fire inspector, but it's something I remember from an early age.
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,971
Location
East Cobb County, Georgia
IRC2012 (which we are under at this time) calls it out in the section called "Fireblocking," so they must have some expectation that's what it does. Many materials (e.g. lumber, plywood, particle board, etc.) specified in the IRC for fireblocking and draftstopping are combustible. They explicitly state the material used for pipe, cable and duct penetrations is NOT required to meet ASTM E 136. The orange Great Stuff meets whatever testing is required and is accepted by most AHJs in my experience. You are not creating a fireproof structure. The point is to SLOW the spread of fire and allow egress.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
We had an in-service for the Broward County (Ft. Lauderdale FL area) county fire inspectors where a NFPA video was shown, where a test was done on wall penetrations. It was a sobering video, as it showed rapid expansion into the other side, of fire gases, which is usually what can kill you, not direct exposure to fire. The penetration was small, I don't recall the exact size, but I believe it was 1/8". The opposite room from the fire source became charged with carbon monoxide moving through the wall penetration, in a matter of minutes, making the room an asphyxiation chamber.

The AHJ is always whom you have to-satisfy. However, if you're protecting your loved ones, above-code is that-much-more protection. You may-not need to do it, but if the cost is minimal, why-not do it?

When I was a youngster, a family down the block had a late-evening house fire, single-family residences in a fairly-new construction area. The two boys were my age and 2 years-older, the older kid was asphyxiated and died. Our home was 5 or 6 years-old by then, and I don't recall the fire's origin, but it was the first time I had someone I knew who died. I don't think it had any cause for me to enter a career as a firefighter/paramedic and fire service instructor and fire inspector, but it's something I remember from an early age.

It's the smoke that kills .. and modern houses with typical construction ... leak like crazy. Another factor is the heat flow and how it pushes and pulls through a building ...

That's why I like spray foam w/ traditional construction -- it works.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Around here, any holes where wires are drilled through a top or bottom plate of a wall, needs to be fire caulked. And it has to be the red stuff. They make a yellow colored fire caulk, which is cheaper, but the inspectors wont accept it. Don't really know why. On plumbing stacks, they flash around it with sheet metal, but on supply lines, they use the caulk. They also make a fire retardant insulation for larger voids in the framing.
 
Last edited:

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,296
Location
Illinois near St. Louis, Missouri
What can be done for conduit from basement to attic? That is very useful for adding things - both low voltage and line voltage so in the past I have put in one for each near the panel of about 1.5 - 2". But filling the end of the conduit with goop that is hard to take out kind of defeats the purpose. Is the clay like putty they make for electrical openings generally accepted for fire stopping? What do people usually use for this? Around the outside of the conduit the sealing is permanent so no issue with rework.
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
Use the red firestop putty. It comes in a 2" diameter tube. You pull out a chunk, and knead it, to soften it. Stuff it in the pipe like duct-seal. It never really hardens.

Steve
 

johnnyradiant

Well-known member
Joined
Mar 27, 2017
Messages
833
Location
Vancouver, BC
It's the smoke that kills .. and modern houses with typical construction ... leak like crazy. Another factor is the heat flow and how it pushes and pulls through a building ...

That's why I like spray foam w/ traditional construction -- it works.

And new houses go through a pressure testing to reduce those crazy leaks. Currently the priority is higher for efficiency but it is also for fire spread. If the real priority was for fire they would likely be limiting some of the materials used/placed in homes for better safer materials, instead of focusing on air leaks.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,565
Location
Northern Virginia
What can be done for conduit from basement to attic? That is very useful for adding things - both low voltage and line voltage so in the past I have put in one for each near the panel of about 1.5 - 2". But filling the end of the conduit with goop that is hard to take out kind of defeats the purpose. Is the clay like putty they make for electrical openings generally accepted for fire stopping? What do people usually use for this? Around the outside of the conduit the sealing is permanent so no issue with rework.

Our tech wire guys run these conduits as well in new homes - they call them future proofs. One of them uses the flexible type conduit, puts an open ziplock bag into the conduit open end with the bag opening to the outside, then sprays fire block foam inside the bag. Another uses hard conduit and slips a plumbers cap on the ends. All I can say is my inspectors seem to be happy with these methods.
 