Spray foam over wiring

6768rogues

Banned
Joined
Nov 28, 2007
Messages
4,524
Location
Western NY
My son has a large barn and he plans to wire it. One thought was to attach Romex to the sidewall girts then insulate and finish the inside of the walls. He might have the sidewalls insulated with spray foam. That would leave the Romex embedded in the spray foam. Will that cause the wiring to overheat?
 
To avoid these ads, REGISTER NOW!

jbberns

Well-known member
Joined
Jan 1, 2012
Messages
105
That is the same as any other insulation in walls. Be fine. Just hard to add anything later.
 
OP
6

6768rogues

Banned
Joined
Nov 28, 2007
Messages
4,524
Location
Western NY
My concern is due to other insulations that are fibrous allowing for some cooling for the wires. Because wires in a bundle are a concern, I thought that perhaps there would also be a concern about having a substantial length of wire encased in a tight cocoon of foam insulation. Thanks for your response.
 

green.bubbly

Well-known member
Joined
Dec 14, 2008
Messages
2,156
Location
Lafayette, LA
I'm no electrical expert but romex doesn't get hot?

From what I understand, you are semi-correct. A properly sized Romex out in the open should not get "hot".

However, there is a concern if several runs are bundled together and surrounded by something like a conduit.

That said, I have not read anything concerning spray foam around Romex.
 
To avoid these ads, REGISTER NOW!

jbberns

Well-known member
Joined
Jan 1, 2012
Messages
105
I wouldn't tie wrap ten together and then spray foam it. But a few of them will be fine.
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
Go for it.
It has been done more times than be counted.
If bad things have happened because of it the regulations would be in place to stop it.

In general, construction codes are very conservative and very reactive.
If you are lucky there is some property rights concern thrown in.

If it is not specifically prohibited, the best guess id that it hasn’t caused any problem in the past.
 

cowboyjosh

Well-known member
Joined
Mar 11, 2010
Messages
1,066
It'll be fine.

In the highly unlikely event a fire starts from overheated wiring covered in spray foam, insurance will build you a spiffy new barn, and you'll know better next time.
 

Td_20

Active member
Joined
Aug 7, 2011
Messages
37
Location
Alberta, Canada
You will be fine as long as you don't over load the circuit.
May be installed in locations with temperatures up to 90°C but with the ampacity limited to that of 60°C conductors

In general, wire should carry current continuously at no more than 80% of its rating.
i.e. 20 amp wire should be loaded to no more then 16 amp continuously.
If your running muitple circuits in a pathway or conduit you you can only run so many of certain size together i.e. 6 of #8awg in 3/4 inch emt conduit.
 
Last edited: