Sprinkler Wire For Thermostat?

DC73

Well-known member
Joined
Dec 27, 2014
Messages
1,627
Location
Lubbock TX
I have some left over 18-7 sprinkler control wire. UL listed for direct burial and 75C.

Would there be any issues with using this wire to connect to the AC/Furnace thermostat in my new shop?

Also, around here, they routinely run the control wire for the outdoor unit into the AC disconnect and through the same hole in the wall for the power cable. Any issues with this approach?

Thanks much,

DC
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
18 is a little overkill, but there's no other reason I can think of not to use it. Just don't use fire sytem wire...

Tommy
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,268
Location
Penngrove, California
Low voltage wire behind wall should be Class 2 or better rated. I am not sure sprinkler wire is.

I would not mix low voltage and 240VAC unless the box is partitioned.

HVAC folks tend to use color codes for fan, heat, common, etc. Not sure if sprinkler wire will have the same colors available. Certainly will work electrically.
 
OP
D

DC73

Well-known member
Joined
Dec 27, 2014
Messages
1,627
Location
Lubbock TX
Low voltage wire behind wall should be Class 2 or better rated. I am not sure sprinkler wire is.

I would not mix low voltage and 240VAC unless the box is partitioned.

HVAC folks tend to use color codes for fan, heat, common, etc. Not sure if sprinkler wire will have the same colors available. Certainly will work electrically.


The needed colors are all there but the gotcha may be the Class 2 requirement. I can't find anything about the wire that indicates the class. Can you educate me about what Class 2 requires?


how much are you saving by using it?

Doesn't matter. I have the sprinkler wire and don't need it. It would be dumb not to use it if it meets code, has the right colors, and is appropriately sized.

DC
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
Class 2 wire is for circuits 24v (max) and 100w (max). Your wire is rated for 30v, so it's higher than Class 2.
Back in the day, 18 AWG was the norm for thermostat wire.
Sounds to me like you're good to go.
CD
 
To avoid these ads, REGISTER NOW!

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,268
Location
Penngrove, California
A real by the book inspector may challenge if class 2 is not printed on the sheath.

I would be more concerned with having low and high voltage in a common box without partition. I am surprised the control wire does not just follow the path of the line set.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Just remember that you shouldn't be using fire system wire for other purposes. It has a red outer jacket to distinguish it.





JBP


.

I mentioned that, too. I think the OP 's "sprinkler" wire is irrigation sprinkler control wire, not waht you and I call "fire wire".

Tommy
 
OP
D

DC73

Well-known member
Joined
Dec 27, 2014
Messages
1,627
Location
Lubbock TX
I would be more concerned with having low and high voltage in a common box without partition. I am surprised the control wire does not just follow the path of the line set.

I won't be running the control wire along the same path as the power cable. I asked the question because that is what is typically done by the "professionals" around here and I was curious if it was acceptable in case I needed to go that route. I actually plan to install some conduit so I can pull the wire later.

I mentioned that, too. I think the OP 's "sprinkler" wire is irrigation sprinkler control wire, not waht you and I call "fire wire". Tommy

Correct.

DC
 

Holt

Well-known member
Joined
Dec 5, 2008
Messages
1,212
Location
Bellevue, Nebraska
The terminals on a thermostat are really ment for small wiring
I'm not sure a thick wire would fit
By the foot the wire is cheap. Get the correct wire just to be safe.
 