Square D HOM Tandem Breaker Ties

AffableCurmudgeon

Well-known member
Joined
Jan 26, 2009
Messages
1,906
Location
Triad Area NC
I am not finding any ties for tandem breakers (pictured). I see ties that work for breakers in 2 different breaker locations, but none that tie the two breakers in the same tandem breaker. I need to tie the two circuits. I am using a m4 nut and bolt. Any better way? Thanks.

1712065283157.jpeg
 
To avoid these ads, REGISTER NOW!

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
Why do they need to be tied together? Just curious...
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
If it isn't in the square d catalog, then you'll be on your own. The bolt you are using should suffice, but keep it mind that it won't cause both to trip if there is an overload or short
 
OP
A

AffableCurmudgeon

Well-known member
Joined
Jan 26, 2009
Messages
1,906
Location
Triad Area NC
Yep, that is what I figured. I just want to make sure that when someone kills the circuit, on purpose, to work on the outlets, they kill both circuits. I have 5 of such boxes, the first one with GFCI and the rest like below.


If it isn't in the square d catalog, then you'll be on your own. The bolt you are using should suffice, but keep it mind that it won't cause both to trip if there is an overload or short
 

Attachments

  • IMG_2974.jpeg
    IMG_2974.jpeg
    167.6 KB · Views: 13

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
It may be a bit of an overthink. If the person has any business being inside the box they will check if it is live before licking their fingers and poking around. If the panel is well labelled it should also take the mystery out of figuring it out (it is two circuits, one location).

If a proper item is not available for the purpose I would not "hack" it. If it was a must for you maybe consider something like the CHOMT2020220 and use the two tied inner breakers as your feed for these two circuits, but you can still wire each with a separate neutral instead of a full MWBC but the two are factory tied for common trip. It will likely require some moving things around on the panel (two spaces required instead of one). It also looks like they make a tie bar for two adjacent breakers like you have, which is a similar concept.

Other than that what you are trying (tying two together, but not MWBC) is likely an uncommon application so off the shelf may not be possible.

Not sure for US code (NEC) but it is not uncommon here for multiple circuits in one box, specially for switches. No need for common trip.
 
Last edited:

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,898
Location
Southern Oregon
OP
A

AffableCurmudgeon

Well-known member
Joined
Jan 26, 2009
Messages
1,906
Location
Triad Area NC
HD has these. About $8 for a package of 3.


They look too big for a tandem, but Schneider shows a tandem in the picture.
Thanks. I looked at those at HD. They work well if you have two tandems side-by-side, one in each breaker slot, and you want to tie the two inner breakers together.
I am just going to stick with the bolt and nut I have in place now. Thanks.
 