It's time to order the electrical gear for our new all-electric home. One Square D i-Line HCN14526 panel board with three QBA222002 thermal magnetic 200A breakers feeding three 225A 40 space load centers. I can have QO load centers/breakers or save some $$ and use Square D Homeline. Any guidance or experience on one over the other?
 
To avoid these ads, REGISTER NOW!

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I was told around 20 years ago when I was opening my shop by a sales rep for sq-d that the qo and home line were identical internally other than the visa trip.
That being said Ive always used the Qo panels on commercial jobs and the Home line stuff for residential jobs.
Ive never had an issue with either style of panel.
 

Notgrownup

Well-known member
Joined
May 5, 2014
Messages
5,924
Location
Snow Hill NC
My wife works for Eaton so I went with Eaton/ Cutler Hammer. I was told the the difference between Homeline and others was minimal...
I don't know if it's true or not. Homeline sells craploads of stuff and we don't hear about the breakers leaking coolant or the drive shaft cracking,,,
I was gonna get Homeline but for 75 bux I got a 24/24 mainlug with 8 20A 2 20a/220, 1 30a/220 & 1 50A/220 delivered.. The Eaton was a no brainer.
 
Last edited:

nick2010tundra

Well-known member
Joined
Apr 20, 2014
Messages
80
Just a little interesting fact about Square D QO breakers. When I built my camp, which is run off solar, the only approved breaker for Dc voltages was Square D. They use a different trip Mechanism than the other brands and it allows them to work on Dc as well.

I Just built and it wasn't a question or an option, SQ D QO or leave my site, I am a lineman and end up at a lot of houses in the middle of the night for bad breakers, never seen a Sq D panel fail
 

Notgrownup

Well-known member
Joined
May 5, 2014
Messages
5,924
Location
Snow Hill NC
Square D is a good brand, no question. When I worked for Crouse Hinds Electrical and we made explosion proof boxes, contractors would spec Square D a lot of the time.
 
OP
L

longez

Well-known member
Joined
Nov 29, 2014
Messages
175
Location
NW Montana
That makes it simple; QO it is. We'll be fairly remote, and getting an electrician out to solve a potential service issue could take days.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,983
Location
Northern Central Ohio
I think you made a smart move going with the QO box. Now in the future if you build a detached garage/shop, use a QO panel in there too. That will allow you to "borrow" a breaker from the garage if one in the home does fail Christmas Eve during a snowstorm.

Even though you've made your decision, I'll still move this for you.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
I've had both QO and homeline breakers fail, as well as other brands. Only difference is the breakers where the QO has orange tab when tripped where homeline doesnt
 

Notgrownup

Well-known member
Joined
May 5, 2014
Messages
5,924
Location
Snow Hill NC
I will now have Cutler Hammer in the shop, GE in the Main panel at the meter box and G\E in the inside the house panel... No issues yet.
 

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
The homeline breakers are wider if memory serves. So if you run a lot of breakers, it takes up more room. Do they make a 40 space homeline?
 

Thumper68

Well-known member
Joined
May 16, 2013
Messages
5,134
Location
Duluth MN
I have always liked the QO, and have them everywhere I can, Makes it nice to only have one style of breaker. Unfortounatly at the lake place I have 3 different kinds, Squared D QO in the shop, in my sisters trailer, panel in my parents cabin and in the power station for guests to plug their trailers into. GE on the pole that feeds my cabin and my parents cabin, and some weird off brand in my cabin.

At some point I will get them all the same, if I live long enough.
 
OP
L

longez

Well-known member
Joined
Nov 29, 2014
Messages
175
Location
NW Montana
This is my last home and am trying to get it "just right" since I'm starting from raw land. The 5,700sf house has a 1,300sf attached garage, but I'm planning for a future 40'x60' shop a couple hundred yards behind us. The i-Line panel box will have (3) 200 amp main breakers for the load centers and a 125 amp main for the future shop. The QO loadcenters and breakers aren't that much more; it may add ~$1K to the house...maybe less. The 600A i-Line panelbox and thermomagnetic breakers are the most expensive electrical gizmos.

I'm having a tough time keeping ahead of the contractor in all the design and equipment decisions, but am sure having fun!
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
The homeline breakers are wider if memory serves. So if you run a lot of breakers, it takes up more room. Do they make a 40 space homeline?

The homeline breakers are no wider than ge full size/ch or any of the other full size breakers on the market,and if its a homeline panel that's what you need to use anyway.
If you have that much stuff to feed will they let you use a 320a meter socket with double taps to feed 2 panels,then feed the 3rd panel as a sub off of one of the others?
Then you could run a 400a service to feed it.;)
 

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
The homeline breakers are no wider than ge full size/ch or any of the other full size breakers on the market,and if its a homeline panel that's what you need to use anyway.
If you have that much stuff to feed will they let you use a 320a meter socket with double taps to feed 2 panels,then feed the 3rd panel as a sub off of one of the others?
Then you could run a 400a service to feed it.;)

I was talking square d where the QO are 3/4" wide and the homeline are 1" wide.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
I was talking square d where the QO are 3/4" wide and the homeline are 1" wide.

Yeah the breakers are bigger but won't interconnect with the same panel, QO will only fit QO, homeline won't fit QO but will fit seimans,Bryant,Murray,ge,and ch br series. Not that it is legal but they do fit. Homeline now has a 42 space panel
 
Joined
Feb 27, 2014
Messages
568
Homeline uses aluminum buss bars and QO uses tin plated copper buss bars. Also QO breaker connection to the buss is much better vs the homeline. Also QO has a limited lifetime warranty and homeline has a 10 year residential warranty.

There are other benefits of QO but more geared to the commercial and industrial environment.

As an electrician Cutler Hammer CH series panels are my top choice, SquareD QO series second then Siemens.
 
To avoid these ads, REGISTER NOW!

Gokart

Well-known member
Joined
May 22, 2010
Messages
177
The new homeline plug on load centers accept tandem breakers anywhere on the bus. The old style only allows you to install tandems in certain locations, however it varies based on the part number
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
In a new installation, nothing says cheap & sloppy like a bunch of twin breakers.
 

redmondjp

Well-known member
Joined
Nov 25, 2014
Messages
2,318
Location
Redmond, WA
In a new installation, nothing says cheap & sloppy like a bunch of twin breakers.

I believe that you are referring to half-thickness circuit breakers.

When you say twin breaker, that could be interpreted as a double-pole breaker which of course is necessary for any 240V loads.

Oh, I vote for the QO as well - we go one better where I work - we use the QOB, where the 'B' stands for bolt-on. Very reliable. Keeps the airplanes safely flying up in the sky (I do the electrical design for the ground-based facilities)!
 

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
Yeah the breakers are bigger but won't interconnect with the same panel, QO will only fit QO, homeline won't fit QO but will fit seimans,Bryant,Murray,ge,and ch br series. Not that it is legal but they do fit. Homeline now has a 42 space panel

You can get QO in larger than 40 spaces also now that the restriction has been lifted.
No discussion of interchange. It was that a larger panel isn't so big with QO breakers. May not be much different with a 20 space. More so with 40
 

Petey156

Well-known member
Joined
Nov 23, 2014
Messages
122
Location
Ohio
Those of you suggesting eaton. Or homeline. You should take your new panel and short out a receptacle with a paper clip, see if it burns one in two, only 2 breakers that won't burn it in half is Qo and pushmatic.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,581
Location
Fullerton, CA
Those of you suggesting eaton. Or homeline. You should take your new panel and short out a receptacle with a paper clip, see if it burns one in two, only 2 breakers that won't burn it in half is Qo and pushmatic.

I think you're ragging on the wrong type of circuit breakers.

Did you mean Federal Pacific Stabloks and Pushmatic by any chance?

Both are well known to make better welders than circuit breakers.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
Those of you suggesting eaton. Or homeline. You should take your new panel and short out a receptacle with a paper clip, see if it burns one in two, only 2 breakers that won't burn it in half is Qo and pushmatic.

Homeline and QO have the EXACT same internals.

Take your ignorance elsewhere.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Those of you suggesting eaton. Or homeline. You should take your new panel and short out a receptacle with a paper clip, see if it burns one in two, only 2 breakers that won't burn it in half is Qo and pushmatic.

So ,did you eat a lot of lead paint chips as a kid?Just wondering why anybody would want to try that stunt?:headscrat:spit:
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,581
Location
Fullerton, CA
Homeline uses aluminum buss bars and QO uses tin plated copper buss bars.

As an electrician Cutler Hammer CH series panels are my top choice, SquareD QO series second then Siemens.

Homeline just uses aluminum buss bars but the QOs have either tin plated copper or aluminum buss bars, depending on what you order.

I agree that the QO breakers are second only to Cutler-Hammer CH.

Longez, the I-line panels are the top of the SqD line not only in residential, but in commercial work too :thumbup:
 

saskscout

Member
Joined
Oct 16, 2011
Messages
10
The new homeline plug on load centers accept tandem breakers anywhere on the bus. The old style only allows you to install tandems in certain locations, however it varies based on the part number

Yes, be careful of this. They can be a real pain to use.

We always use Square D, never any issues.
 

rexer

Well-known member
Joined
Sep 4, 2012
Messages
195
Location
Earth
Changed my panel last year after having several issues from the original 1989 Crouse-Hinds.
(junk & a fire hazard).

It's a Square D QO 200AMP 30/40 .

Home-line breakers are 1" & QO's are 3/4". I also had a space issue, so I went with the QO's, panel is 30" tall . The price difference between the panel box & 23 breakers was about $90.

Worked out great..
 
Last edited:

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Old thread I know, but this is the newest one of many on this topic.

I was surprised to find a 200A Homeline panel in my new commercial space. I don't object to saving money on breakers but I'm wondering how the aluminum bus bars can show up as a weakness. I will occasionally be using a welder or plasma cutter, and there will be a compressor (not sure of the size, but now on a 30A or larger breaker that trips in the cold). Otherwise, nothing that deviates much from residential use.