Hi all
Here's the situation
Live in PacNW. Area I'm in has frequent power outages. We just had cyclon and are on day 3 no power and more to come.
House is 4100sf, multiple refrigerators, regular utilities, inverted heat pump (I bought this one 2 yrs ago on purpose, as it has low power draw). HP has 10KW Aux heat strip.
I have 20KW standby generator installed and connected via 2 automatic switches. Entire house, everything.
I have 25KW transformer from utility company in my property.
Here's my question.
My generator powers everything just fine, AC included. Problem is, if Aux heat strip kicks in, it bogs, almost stalls. Basically, I dicontinued heat strip yesterday via T-stat white wire and HP keeps house at 69D without issue.
But, winter is coming and I'd rather have that heat strip functional as HP struggles with heat, when it gets real cold outside.
And we WILL have more outages when it will snow.
System has no issues, with Aux heat strip On, when running on external power via that 25KW transformer.
I do not mind upgrading generator but, what do I upgrade it for, to safely run heat strip? I'm on propane tank, that limits options, I'm not going diesel or gas one.
That said, will 26KW propane generator suffice? 30? 30s start looking quite spendy too.
Thank you