I am getting ready to install a 9k BTU mini-split. I have a vac pump and a new CPS VG200 micron gauge. The instructions I have read say to use a couple of valve core removal tools, a vac pump and micron gauge then pull a vac to around 200 microns, valve off the vacuum pump and turn it off. Then let the system set with the micron gauge still on the suction access port and wait for 10 minutes. If the vacuum hasn't risen by more than 200 microns then everything is good and you are ready to release the refrigerant from the system.
I wanted to test the pump, hose, valve core removal tool and the micron gauge before I hooked it up to the mini-split. The pump easily pulled a 200-220 micron vacuum. I then valve off the micron gauge, turn off the pump and the VG200 reading starts to rise. In about 10 minutes it went fromm 210 to 380. I assumed there was some leakage around the valve on the valve core removal tool so I tried again. This time I turned the valve on the valve core removal tool at 200 micron but left the vacuum pump on (so it was keeping a vacuum on the hose that is on the other side of the valve core removal tool). Ten minutes later it was at 370. Since it isn't leaking past the valve on the VCRT, it seems to me that it must be leaking where the VG200 connects to the VCRT, which is just a male flare. I have tried two different VCRTs and the results were the same. I plan on buying some nice Appion VCRTs, but since it isn't leaking past the valve, I'm not sure how that will help. Any ideas why this is happening?


I wanted to test the pump, hose, valve core removal tool and the micron gauge before I hooked it up to the mini-split. The pump easily pulled a 200-220 micron vacuum. I then valve off the micron gauge, turn off the pump and the VG200 reading starts to rise. In about 10 minutes it went fromm 210 to 380. I assumed there was some leakage around the valve on the valve core removal tool so I tried again. This time I turned the valve on the valve core removal tool at 200 micron but left the vacuum pump on (so it was keeping a vacuum on the hose that is on the other side of the valve core removal tool). Ten minutes later it was at 370. Since it isn't leaking past the valve on the VCRT, it seems to me that it must be leaking where the VG200 connects to the VCRT, which is just a male flare. I have tried two different VCRTs and the results were the same. I plan on buying some nice Appion VCRTs, but since it isn't leaking past the valve, I'm not sure how that will help. Any ideas why this is happening?