Stimied on dead recepticals

oldwino

ALLIANCE MEMBER
Joined
Nov 16, 2009
Messages
1,917
Location
Sonoma County California (wine country)
Not an electrician here but I’ve done my fair share

Situation is I have two exterior outlets on adjacent side of the house that both went dead after several years. All breakers are on and everything on a GFI inside is working. Other exterior outlets work fine. Traced to no power at these two dead indians but looking for a hint as to where damage may be

Thanx guys



Mod edit: Threads merged/ double post deleted.
 
Last edited by a moderator:
To avoid these ads, REGISTER NOW!

Dumber than lumber

Well-known member
Joined
Dec 19, 2015
Messages
2,050
Not an electrician here but I’ve done my fair share

Situation is I have two exterior outlets on adjacent side of the house that both went dead after several years. All breakers are on and everything on a GFI inside is working. Other exterior outlets work fine. Traced to no power at these two dead indians but looking for a hint as to where damage may be

Thanx guys
Those problem outlets: are they GFCI? Not clear to me from your post.
 

PelicanPines

ALLIANCE MEMBER
Joined
Apr 30, 2014
Messages
38,255
Location
New Jersey, USA, Earth, My own reality
It could be a pain... but see if you can figure out which outlet "Feeds" the two outlets that are dead. The outlet (that may work) that feeds the dead ones... might have an issue.

I live by the ocean... stuff corrodes horribly sometimes. All you need is a hurricane or over zellous pressure washing.

I personally have ONE GFI outlet inside my garage and all the exterior outlets are daisy chained on the feed side of the GFI. So outside the receptacles are "Normal" but are fed by a GFI so they will respond to a Ground Fault.

So 2 things... see if you can find the GFI that feeds the outside... see if you can find the outlet that feeds the two dead ones.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Internet Guess # 1

Those two dead outside outlets are being fed off another GFCI outlet or circuit that you have yet to locate???????? That other GFCI outlet/circuit is tripped. Garage, basement, kitchen counter or bath is the common hiding spot.
 

Los_Control

Well-known member
Joined
Jul 28, 2020
Messages
191
Location
West Texas
When you look at the side of a outlet, there is a tang that connects top to bottom.
Very useful, you can remove it and wire top & bottom different ... top on a switch etc...

Point is, if the outlets are wired together, the tang can burn out much like a breaker tripping.
I had just wired up some new outlets and a light to the attic access ... not a electrician, but know enough to follow code on breaker & wire sizes & matching outlets.
Anyways the tang on the new outlet blew, just poor quality. Everything after it was dead.
I replaced it 15 years ago and no problems since ... just first & last time ran into it.

Find the breaker that runs that circuit, check the power at the nearest outlet to them ... if one has power on top but not bottom, could be it. Depends how it was wired but is a idea for a strange issue.
 

Wrench97

Well-known member
Joined
Jun 23, 2018
Messages
12,431
Location
Southeastern Pa
Usually I find another outlet upstream that uses back stabbed connections and blew the one out that feeds these outlets.
Be careful with the "dead" ones as it may be the neutral that is dead and the hot is still live(you can check between the hot and ground wire to find out).
 
OP
O

oldwino

ALLIANCE MEMBER
Joined
Nov 16, 2009
Messages
1,917
Location
Sonoma County California (wine country)
Forgot to mention, I believe these are on a GFI. Unfortunately electrical has been modified by previous owner and stuff isn’t all marked out correctly. I have verified that all recepticals are live except these two. Los Control may have something with a blown tang on the upstream end. Will check this possibility
 
To avoid these ads, REGISTER NOW!

Dustball

Well-known member
Joined
Jun 25, 2011
Messages
2,081
Location
Hudson, WI
I ran into a similar situation- turned out to be a loose neutral wire in a daisy chained back-stabbed duplex just upstream of the dead one.
 

Dustball

Well-known member
Joined
Jun 25, 2011
Messages
2,081
Location
Hudson, WI
I ran into a similar situation- turned out to be a loose neutral wire in a daisy chained back-stabbed duplex just upstream of the dead one.
 

Yankeefarmer

Well-known member
Joined
Jul 25, 2011
Messages
1,231
Location
Connecticut
My daughter complained of a dead overhead light fixture in her kitchen. Months earlier, I had discovered that the light was fed from a GFCI outlet installed by the previous owner. This time, though, the GFCI receptacle would “test” and reset normally, the receptacle itself was fine, but there was no juice across the load terminals for feeding downstream devices. I hadn’t seen a GFCI outlet fail in that manner before.
 
OP
O

oldwino

ALLIANCE MEMBER
Joined
Nov 16, 2009
Messages
1,917
Location
Sonoma County California (wine country)
Frustrating!
Every receptical inside and out is hot except these two. Weird thing is neither is at the end of a run. I’ve pulled out 6 and none are backstabbed so don’t think it’s a loose connection. Thinking I may pull off an existing/working outlet and rewire these with known power
 

Los_Control

Well-known member
Joined
Jul 28, 2020
Messages
191
Location
West Texas
yeah you need to check the wires going in to the outlet .... not the outlet. Find where the power stops.
But yes is not easy as installed wiring is not easy to get to.
 

welder4956

Well-known member
Joined
Apr 8, 2010
Messages
3,113
Location
Birmingham, AL USA
Not an electrician here but I’ve done my fair share

Situation is I have two exterior outlets on adjacent side of the house that both went dead after several years. All breakers are on and everything on a GFI inside is working. Other exterior outlets work fine. Traced to no power at these two dead indians but looking for a hint as to where damage may be

Thanx guys



Mod edit: Threads merged/ double post deleted.

These two must be fed from another outlet nearby. Look inside the boxes for the closest receptacles inside the house to see if the feed comes from there. I would suspect a loose wire or bad receptacle upstream, or possibly a wire chewed through by a rodent.

You might also plug one of these in the dead receptacle and start checking others nearby:

https://www.amazon.com/Klein-Tools-ET310-Circuit-Integrated/dp/B07QNMCVWP/ref=asc_df_B07QNMCVWP/?tag=hyprod-20&linkCode=df0&hvadid=344005018279&hvpos=&hvnetw=g&hvrand=258522675320281056&hvpone=&hvptwo=&hvqmt=&hvdev=c&hvdvcmdl=&hvlocint=&hvlocphy=9012570&hvtargid=pla-738005504290&psc=1&tag=&ref=&adgrpid=69357499415&hvpone=&hvptwo=&hvadid=344005018279&hvpos=&hvnetw=g&hvrand=258522675320281056&hvqmt=&hvdev=c&hvdvcmdl=&hvlocint=&hvlocphy=9012570&hvtargid=pla-738005504290
 