This storage shed was built long before we purchased the house, 15 years ago. I recently leveled it and put new siding on it. Size is 14x10. There is roughly 25 ft of conduit under ground with romex running from main circuit panel on the house, 20 amp breaker, to the shed. No ground rod was used. We live in a rural area where most everything is done without a permit. The only thing electrical I plan to use are lights, receptacles, and maybe a bench grinder. Would you guys recommend new wiring and/or conduit to the shed?
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
If the wire is nm-b it should be replaced with wire approved for outside and below ground use. If it's uf-b then it's okay. Capacity wise what you have is probably okay.
Depending on the age it may not have the "-B" suffix. That started in the mid 1980's, with the suffix it has 90°C conductors, without they are rated for 60°C, although both still sized based on the 60°C ampacity. Still a good call to remove if NM cable was pulled through a UG conduit.
 

Spud McGee

Well-known member
Joined
Apr 11, 2022
Messages
405
I'd use the existing wire to pull new wire, just for the fact that you'd get a ground. 12ga, 20 amp single breaker seems more than fine for that size unless you know you have a need for bigger.

Depending on what you're plugging in, you may not even need a ground. Chargers for lithium batteries only have 2 prongs. A ground wire wouldnt add anything. If you do need to be able to plug in 3 prong plugs, it is up to code in NEC and here in GA to install 3 prong outlets even with no ground wire. You must put an arcfault breaker in the panel and a little sticker on the outlet showing that the ground pin is not functional.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
If you keep it to a single circuit, you don't need the ground rod.

Personally, if the wire need to get replaced, I would run a multi wire brand circuit (mwbc) which only necessitates a single additional conductor and will give you a second circuit. If there is conduit end to end, thwn is the ticket. Black white, red and a green. Replace the breaker with a two pole 20a.

If the wire is UF, I'd leave it be and just have the single circuit unless you want more.

Regardless what you do, you should have the circuit first go to a gfci receptacle so you are protecting everything downstream
 

KenC

Well-known member
Joined
Dec 20, 2009
Messages
2,604
Location
oklahoma
I'd use the existing wire to pull new wire, just for the fact that you'd get a ground. 12ga, 20 amp single breaker seems more than fine for that size unless you know you have a need for bigger.

Depending on what you're plugging in, you may not even need a ground. Chargers for lithium batteries only have 2 prongs. A ground wire wouldnt add anything. If you do need to be able to plug in 3 prong plugs, it is up to code in NEC and here in GA to install 3 prong outlets even with no ground wire. You must put an arcfault breaker in the panel and a little sticker on the outlet showing that the ground pin is not functional.
I think you meant to say GFCI, not arc fault. And it can be done with a recpt which is cheaper than a breaker and can feed downstream recpts if needed and that's where the sticker comes in.
edit to add: if the conduit is in good condition, I'd use THWN, not UF. If metal conduit it can also be used as the grounding conductor If plastic, or you just want to, add a third wire, (green)
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
12,039
Location
Austin, TX
The only thing electrical I plan to use are lights, receptacles, and maybe a bench grinder. Would you guys recommend new wiring and/or conduit to the shed?
There's a code issue if it's NM-B. Personally, that would be last on my honey-do list and would not worry about it. The only way I'd recommend a re-do is if you blow that 20A breaker. Not blowing that breaker, you've probably got better things to do.

Need 240V or adding heater/HVAC - then I'd pull 10ga and do a very small sub panel.
 
OP
4

4 Ever-Fish N

Well-known member
Joined
Jul 20, 2011
Messages
350
Location
Deep East Texas
Here's a couple of pictures of the wiring. One thing I forgot to mention is I do want to install a small AC unit.
 

Attachments

  • storage shed wiring.jpg
    storage shed wiring.jpg
    62.9 KB · Views: 99
  • storage shed wiring 2.jpg
    storage shed wiring 2.jpg
    74 KB · Views: 98

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
Nothing. I couldn't even find anything that looked like letters.
I bet it is embossed in the jacket and not printed.

Anyplace you can easily open up? I had some UF that looked a lot like what you have, the telltale was when you stripped the outer jacket it was molded to the inner insulation.
 
To avoid these ads, REGISTER NOW!

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,442
Location
Western North Carolina
One thing I forgot to mention is I do want to install a small AC unit.
I have a similar sized shed powered by a 15a circuit and it runs a window a/c and a small tool, a full sized stereo plus bunch of lights.
The shed is insulated though but sits out in the open in full sun.
So my guess is 20A should do the trick.
 
OP
4

4 Ever-Fish N

Well-known member
Joined
Jul 20, 2011
Messages
350
Location
Deep East Texas
I am pretty sure the wiring I have is NM. When squeezing the cable, I could feel the wires move around and the ground wire is wrapped in paper. I took a picture of the end of the wiring before it connects to the light. Your thoughts?
 

Attachments

  • storage shed wiring 3.jpg
    storage shed wiring 3.jpg
    490.7 KB · Views: 61

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
What would you recommend for a 25 to 30 ft run underground? I always prefer to go a step above minimum. Thanks.
For a single circuit? If you are doing conduit end to end, #12 thwn. No reason to go thicker than that.

I'd add an extra hot and run a mwbc for two separate 20a circuits. Only added cost is another piece of wire, a two pole breaker instead of a single pole and one extra gfci.

If you wanted to run a small subpanel, #10 thwn would add some capacity
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,942
Location
Central New Jersey
Is the wire you have shown, with the paper around the ground (which is NM) the same wire that is coming up out of the ground in the conduit? You posted two pictures in post number 13, one that shows a single cable coming out of the ground in conduit, and another picture that shows two sets of wires connected to a box. Is that where the wire coming up from the ground/conduit terminates? You need to check the cable coming out of the conduit to see if it is UF-B. If it is, then you can, by code, run the things inside the shed using NM-B. UF-B was jacketed in white, and a few other colors, before the universal color of gray was put into place. If the cable coming up from the conduit does not have any colored printing on it, use a flashlight and shine it along the cable from both sides to light up the raised areas where the writing will be embossed on it. This will help to highlight the letters so you can read it. The cable coming up from the conduit may not be the same cable used to wire the light fixture you have shown in post 26. If it does end up to be NM cable in the conduit coming up from the ground, then you have to replace it with either UF-B or thwn wires as others have said.
 
Last edited:

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I'd use the existing wire to pull new wire, just for the fact that you'd get a ground. 12ga, 20 amp single breaker seems more than fine for that size unless you know you have a need for bigger.

Depending on what you're plugging in, you may not even need a ground. Chargers for lithium batteries only have 2 prongs. A ground wire wouldnt add anything. If you do need to be able to plug in 3 prong plugs, it is up to code in NEC and here in GA to install 3 prong outlets even with no ground wire. You must put an arcfault breaker in the panel and a little sticker on the outlet showing that the ground pin is not functional.
What you're describing is only acceptable/up to code if you're replacing old, existing, 2-prong receptacles with new 3-prong receptacles, and there's no grounding conductor available to connect the receptacle to. It is not acceptable or up to code if you're installing a new circuit or replacing existing 3-prong receptacles. See 406.4
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,241
Location
Modesto, CA
I'd use the existing wire to pull new wire, just for the fact that you'd get a ground. 12ga, 20 amp single breaker seems more than fine for that size unless you know you have a need for bigger.

Depending on what you're plugging in, you may not even need a ground. Chargers for lithium batteries only have 2 prongs. A ground wire wouldnt add anything. If you do need to be able to plug in 3 prong plugs, it is up to code in NEC and here in GA to install 3 prong outlets even with no ground wire. You must put an arcfault breaker in the panel and a little sticker on the outlet showing that the ground pin is not functional.
not quite. it needs to be a GFCI breaker or receptacle not an AFCI... an AFCI wont give 2 craps about a ground fault...
 
Last edited:
OP
4

4 Ever-Fish N

Well-known member
Joined
Jul 20, 2011
Messages
350
Location
Deep East Texas
The wire comes out of the conduit and into a switch box. The attached photo shows the wire on the left side of the box coming in from the bottom. You can see the paper wrapped wire, but you may have to zoom in.Wiring entering storage shed.jpg
 