I am running six new 220 circuits in conduit to some feed bin fans, unloading augers, etc next to my detached garage. The motors pull 8-17 amps (FLA) and are 75-80 feet from the panel so I'm using 10ga wire. I purchased spools of black and yellow 10ga stranded THHN, and I'm wondering if I can run a smaller gauge like 14ga for my ground wire to save a few bucks? Also, is OK to use stranded wire for ground? Thanks!
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,179
Location
Modesto, CA
Backup.

Wire for Motor circuits is sized by HP NOT FLA.

So what is the HP rating on the motor?

What voltage? Single phase or 3 phase?
 
To avoid these ads, REGISTER NOW!
OP
N

Nomechanic

Member
Joined
Sep 6, 2011
Messages
9
Location
Spring Valley, OH
Thanks for your replies. Sorry I didn't provide enough info. I'm wiring to the following motors:

(2) fan motors - 3hp / 1ph / 230V
(4) auger motors - 1hp / 1ph / 230V (Baldor farm-duty)
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
What kind of pipe? The wire size is good. All in one pipe? You only new 1 per pipe. If in 1 there could be possible creating issues but this is likely not much a real issue, all running at once? Since some are only 1hp not so much a problem and if there was a problem meeting the letter of it could be done with a breaker change. Wylie could elaborate better than I could.
 