Stubbing into pole barn

jeepnatv4life

Well-known member
Joined
Nov 26, 2013
Messages
196
Location
Harrisonburg Area VA
I have ran all my stubs into my pole barn.... (electric,Cat5,and another electic to power a nearby shed) My question is do I need to have a ground rod stubbed up thru my slab also???
 
To avoid these ads, REGISTER NOW!

Pwrgeek

Well-known member
Joined
Oct 18, 2015
Messages
288
Location
Texas USA
If you are planning a sub panel then you need a Grounding Electrode System. Two ground rods works or a Ufer.


Sent from my iPhone using Tapatalk
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Your ground rods must have their entire 8' length in earth. No part of it can stick up out of the ground or be embedded in concrete. We usually drive two rods outside, then we'll bring the wire from the rods and ziptie it up the side of the conduit feeding the panel.
 
To avoid these ads, REGISTER NOW!

Chris705

Well-known member
Joined
Nov 1, 2012
Messages
834
Location
The Finger Lakes of NY
#6 copper ground wire can go thru your wall to get to the ground rods. (Doesn't have to be in conduit) Use the clamps that force the copper wire tight to the ground rod. Not the ones that have a set screw style where you put the wire thru a separate hole. I just went thru my sub panel rough in inspection. Ready for final now.
 