sub feed to garage

al704

Member
Joined
Jun 10, 2014
Messages
24
existing detached garage is subfeed with 3 wires, 2 hot, 1 neutral. Ground bar goes to ground rod, is this acceptable?
 
To avoid these ads, REGISTER NOW!
OP
A

al704

Member
Joined
Jun 10, 2014
Messages
24
no idea when it was installed, not concerned with passing inspection. Is it safe this way? Any possible issues?
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,126
Location
SE MI
It is NOT current code.

That being said, there are millions of garages wired that way. You don't hear about a lot of them burning down !

I would change the 120V duplex outlet to GFCI before I would worry about installing a 4 wire feed.
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
existing detached garage is subfeed with 3 wires, 2 hot, 1 neutral. Ground bar goes to ground rod, is this acceptable?

By any chance is the feed in conduit? Steel? or if PVC could you pull another wire in ?

You said its been installed for a long time, possibly met code requirements (as stated above) when it was installed, I would have to look when the NEC changed to 4 wire sub panel feeds, I'm sure someone here knows off the top of their head!!
 
Last edited:
To avoid these ads, REGISTER NOW!

dartworth

Active member
Joined
May 4, 2016
Messages
26
Location
Cleveland
It is NOT current code.

That being said, there are millions of garages wired that way. You don't hear about a lot of them burning down !

I would change the 120V duplex outlet to GFCI before I would worry about installing a 4 wire feed.

Just curious, what is the current code?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
If the feeder is large enough for the load, leave it alone, but the grounding electrode must be connected / bonded to the neutral. If upgrades are needed then it will need to comply with current codes.
 