Hello, I need to add a few sub panels to my shop. I have one square d NF 250 amp 480/277 panel and I need to get another NF panel. So I have been looking for another (probably used panel) I assume I can use a higher rated panel ( 600v/348 ) on my system? Also the panel I have and most of them I'm looking at are / rated. My service is 4 wire Wye 480, but I don't need 277V from these sub panels, so I'm not going to run 4 wires to them, and probably will remove the grounded conductor bus from them. I have noticed some panels are marked 480/277 4 wire and 240v 3 wire ( I assume for a delta service and 240v to ground). I also assume that I don't need a 480v delta 3 wire rated panel as I can't not generate the 480v to ground that requires one even though I will only be running 3 wires??

Thoughts??

Thanks
William.....
 

Attachments

  • 20240318_012359.jpg
    20240318_012359.jpg
    646.5 KB · Views: 18
To avoid these ads, REGISTER NOW!
OP
W

W-Cummins

Well-known member
Joined
Jan 9, 2006
Messages
1,641
Location
Iowa
I would not touch you job, IMHO you are being unreasonable in your expectations.
Well I'm not looking for some one to wire the sub panels.... can you expand on why you think I have unreasonable expectations? You don't think the Square D NF panel's are up to the task?
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,003
Location
Coronado, CA
Well I'm not looking for some one to wire the sub panels.... can you expand on why you think I have unreasonable expectations? You don't think the Square D NF panel's are up to the task?
Electrical Equipment is required to be installed and used inaccordance with the manufacturers instructions.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,758
Location
NW Iowa
I don't see an issue with it. I would assume you are planning on a ground wire even though it's not mentioned. I would bond the neutral buss and mark it equipment ground only.

Downside of a higher rated breaker is if you need to purchase a new breaker, the cost will be more.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
You can't use slash rated equipment, 480/277V, on 480V systems, since your 480/277V, your good to go on that point. BTW it's 600/347V, common in Canada.
 

Steve from Socal

Well-known member
Joined
Jan 27, 2009
Messages
3,499
Location
Hutchinson Ks.
What do you need for used? I have a nice 400 amp main lug I-line panel and several three pole breakers These are in Hutchinson, Ks they could sip via Fastenal freight
 

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,072
Location
Fernley, Nevada, about 30 miles east of Reno.
I've been a commercial/industrial electrician for more than 30 years. I've installed a number of panels like you're describing.

I make some sort of a placard that states '480 VOLTS 3Ø 3 WIRE. 277 VOLTS NOT AVAILABLE.'

Also, I remove the neutral bus.

A lot of my work is inspected, never had a problem.

The ratings are maximum, actual conditions can be lower. I've done jobs that were 120/208 and the available fault current exceeded what 120/240 breakers could handle. The engineer specified 277/480 panels and breakers and a placard stating '120/208 VOLTS 3Ø 4 WIRE Y'.

I would have no problem at all doing what you describe, just mark the 3 wire panels as having no 277.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
Hello, I need to add a few sub panels to my shop. I have one square d NF 250 amp 480/277 panel and I need to get another NF panel. So I have been looking for another (probably used panel) I assume I can use a higher rated panel ( 600v/348 ) on my system? Also the panel I have and most of them I'm looking at are / rated. My service is 4 wire Wye 480, but I don't need 277V from these sub panels, so I'm not going to run 4 wires to them, and probably will remove the grounded conductor bus from them. I have noticed some panels are marked 480/277 4 wire and 240v 3 wire ( I assume for a delta service and 240v to ground). I also assume that I don't need a 480v delta 3 wire rated panel as I can't not generate the 480v to ground that requires one even though I will only be running 3 wires??

Thoughts??

Thanks
William.....
nope you dont need a straight rated delta 480v panel because you have 4870Y/277v service. The straight rated delta panels have higher ratings because 240v and 480v to ground has higher fault current.

But a slash rated 480v panel is the proper panel to use.
 
To avoid these ads, REGISTER NOW!

klassenl

Well-known member
Joined
Feb 20, 2016
Messages
715
Location
Southern Alberta
The ratings are maximum, actual conditions can be lower. I've done jobs that were 120/208 and the available fault current exceeded what 120/240 breakers could handle. The engineer specified 277/480 panels and breakers and a placard stating '120/208 VOLTS 3Ø 4 WIRE Y'.
I find that interesting. In my part of Canada that would not pass.


I will ask my inspector or engineer about this kind of thing the next time they are chatty.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
I find that interesting. In my part of Canada that would not pass.


I will ask my inspector or engineer about this kind of thing the next time they are chatty.
It may have been that 42K or 64K interrupting current rated breakers were impossible to get w/ a 120/240V rating, but were in stock with a 277V or 480/277V rating, I cannot see operating a panelboard, & breakers under their rated voltage as a safety issue.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,758
Location
NW Iowa
It may have been that 42K or 64K interrupting current rated breakers were impossible to get w/ a 120/240V rating, but were in stock with a 277V or 480/277V rating, I cannot see operating a panelboard, & breakers under their rated voltage as a safety issue.

The breakers and panels are usually rated and tested for the lower voltage as well as the higher voltage.

Pretty sure the breakers usually list AIC for 480 and then separate line listing a higher AIC at 240
 
OP
W

W-Cummins

Well-known member
Joined
Jan 9, 2006
Messages
1,641
Location
Iowa
I don't see an issue with it. I would assume you are planning on a ground wire even though it's not mentioned. I would bond the neutral buss and mark it equipment ground only.
Yes I'm planing on a 4 gauge ground conductor ( for >200amps).
I'm planing on running main breaker panels w/225 amp 480v 65ka KLC34255's

So sense I started on this Delta power, down the internet rabbit hole journey, and I now have been looking into ungrounded delta systems, I have a new question:)

If I run the 3 wires from my 4 wire Wye system to a sub panel serving my plasma table ( with an additional at the table ground rod) and some how the ground feeding the panel from the main switch board gets cut/removed/etc... will I have a un-grounded delta at that sub panel??

You can't use slash rated equipment, 480/277V, on 480V systems, since your 480/277V, your good to go on that point. BTW it's 600/347V, common in Canada.
I was reading some place that there are also some 600/347 systems in up state New York, that might be why I'm seeing panels for sale with that rating in the NE US?
I've been a commercial/industrial electrician for more than 30 years. I've installed a number of panels like you're describing.

I make some sort of a placard that states '480 VOLTS 3Ø 3 WIRE. 277 VOLTS NOT AVAILABLE.

That sounds like a good idea I will mark them
Also, I remove the neutral bus.

So I have one vote for remove and one for re-use for the eq grounds, I was thinking that I will only have 14 breakers in the boxes, I would not need the HD connections of the grounded conductor bus bar, and if I cut the can/eq ground bus off to 14 positions it would discourage anyone from using it as a neutral.
 

Attachments

  • 20240318_012439.jpg
    20240318_012439.jpg
    500.6 KB · Views: 4

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
No you wouldn't have an ungrounded delta simply because an EGC is missing. The neutral is still bonded at the main switchboard.

If you wanted ungrounded delta you would have to setup a separately derived system along with ground fault detection equipment which could be as simple as 3 480v industrial bulbs wired in wye.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
Ungrounded means there's no connection to ground at the source. If the source is grounded then the entire system is considered grounded.

Also, if the system is Y at the source, it is always Y unless there's a transformer with a ∆ secondary.
not for a separately derived system that is isolated.

yes he would need a delta-delta transformer.
 