Sub panel grounding

Kinger

Well-known member
Joined
Oct 6, 2006
Messages
81
Location
Southern WI
I installed a main lug panel in my attached garage this weekend.

The question I have is, it did not come with a grounding strip. I picked up an equipment grounding strip on a another trip to the store. It does not fit the mounting holes. Has anyone run into this before?

I have read through the numerous posts here and on other forums online. If I am understanding things correctly, I need to have a ground bar in the main lug, to maintain the grounding from the main panel.

I installed:
Square D Homeline, 100 Amp main lug
I used 8/3 wire (thought that is what the electrician recommended for 60 amps, but I think I might have shorted myself).

Thanks
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Technically you should have a 40A breaker in front of that wire, 6-3 w/g would have been far superior breakered at 50A. In the sub, you do not install the green bond screw that came with the panel in the neutral bar but all the grounds are connected together and bonded to the box via the bar attached with threaded screws or bolted to box. (no self drillers allowed to connect grounds)
 

Attachments

  • panel shed 1.JPG
    panel shed 1.JPG
    32.5 KB · Views: 137
Last edited:
OP
K

Kinger

Well-known member
Joined
Oct 6, 2006
Messages
81
Location
Southern WI
Technically you should have a 40A breaker in front of that wire, 6-3 w/g would have been far superior breakered at 50A. In the sub, you do not install the green bond screw that came with the panel in the neutral bar but all the grounds are connected together and bonded to the box via the bar attached with threaded screws or bolted to box. (no self drillers allowed to connect grounds)

Thanks for the reply.

I did not install the bonding screw. The bonding bar for the grounds is what doesn't line up with the holes to be threaded into the box. I will have to try and bolt it or see if they sell a longer one that would line up with the holes.

I may bite the bullet and repull the wire. Just don't tell the wife!
 

LoneGunman

Well-known member
Joined
Mar 27, 2007
Messages
2,081
Location
The Gunshine state
Drill a hole in the panel and thread the hole for your mounting screw, as sberry stated, self tappers are not allowed.

What size breaker is feeding the 8/3 from the house?

*nevermind, reread your post. You need to either repull it with the correct wire or drop the breaker size. Why not go for 100 amp, long run?
 
Last edited:

Terry Kennedy

Well-known member
Joined
Feb 4, 2008
Messages
80
Location
Northern NJ
The question I have is, it did not come with a grounding strip. I picked up an equipment grounding strip on a another trip to the store. It does not fit the mounting holes. Has anyone run into this before?

Square D Homeline, 100 Amp main lug

I'm not sure about the Homeline series, but the QO series panels have a huge number of grounding strips, not all of which work in all panels.

Ok, after looking, here is the Homeline list. Pick the correct grounding strip for your panel. Probably a PK7GTA which has only 7 positions, so you may need more than one.
 
OP
K

Kinger

Well-known member
Joined
Oct 6, 2006
Messages
81
Location
Southern WI
What size breaker is feeding the 8/3 from the house?

*nevermind, reread your post. You need to either repull it with the correct wire or drop the breaker size. Why not go for 100 amp, long run?

In reality I don't think I would ever use the load, plus I was trying to save some money. (That option is out the window if I repull wire)

I mostly do light car and motorcycle repair/maintenance. I don't foresee a lift in the near future, probably never at this house. I really only think I might get a 220v compressor in the future. I know things change.........


I'm not sure about the Homeline series, but the QO series panels have a huge number of grounding strips, not all of which work in all panels.

Ok, after looking, here is the Homeline list. Pick the correct grounding strip for your panel. Probably a PK7GTA which has only 7 positions, so you may need more than one.

Thanks. I bought the PK15GTA. I will pick up two 7GTA's next time I go to the store.

Thanks
 
To avoid these ads, REGISTER NOW!

Terry Kennedy

Well-known member
Joined
Feb 4, 2008
Messages
80
Location
Northern NJ
Second question:

Is it worth setting up a main breaker in the sub panel?
It is a handy way to shut everything off at once. I would do it whenever the subpanel is not adjacent to the panel that feeds it.

However, main breakers can get *very* expensive. On the QO 40-position panel, the panel (including 200A main breaker) was $192 at Home Depot, but the best price I could find for a 100A main breaker alone was $194 at Grainger.
 

JohnK007

Well-known member
Joined
Sep 13, 2007
Messages
807
Location
Downers Grove, IL
I have 8/3 feeding a four position sub panel in my detached garage. It's connected to a 40 amp breaker at the main. Largest circuit in the garage is a 30A 220 that fed my welder, but now feeds a 5000W electric heater. The other two manage the lights and wall receptacles.
My point is I think 40A is the best you're going to get out of 8/3. But don't despair. If you're not pulling a high, sustained load, 40 amps is a lot of juice. Why not give it a try for a while and see if you trip the breaker a lot. You can always re-pull later.
 

prestonjrf

Member
Joined
Sep 3, 2008
Messages
15
Location
Ms
Will removing one of the screws in another space line it up? If so just put the lug screw in the leftover spot.
 