The grounds and nuetrals were wired that way when I bought the house.
Why do they need to be separate if they are on the same bar? Connection issue?
One day if Im feeling froggy Ill separate them.
Thanks guys!
The grounds and nuetrals were wired that way when I bought the house.
Why do they need to be separate if they are on the same bar? Connection issue?
One day if Im feeling froggy Ill separate them.
It's a listing requirement of the panel to having only one grounded conductor (neutral) per terminal. To carry more than one conductor the terminal has to be identified as such.
Recent changes (2008 NEC, iirc) prohibit more than one neutral (grounded conductor) under one terminal. Prior to this NEC change it was based on manufacturer instructions/ listing. It was likely perfectly acceptable when this panel was installed. And perfectly safe IMO.
The NEC 2014 110.14(A) just says terminals for more than one conductor shall be so identified.
Edit: The code still leaves it to the equipment listing. 2014 NEC 110.3(B)
Edit Edit: There is code that limits grounded conductor to one per terminal. 408.41. I was thinking it was only limited by the panel listing because you never see listings allowing more than one grounded conductor per terminal. Live and learn.