Sub panel off meter base

mkbrower

Active member
Joined
Aug 11, 2010
Messages
44
Location
Foot Hills of North Carolina
Is there a NEC rule that states you can only have one panel fed off the load side of the meter base. It was my understanding you could have multiple panels off the meter base as long as the total load amps does not exceed the supply amps.

When I wired my shop, I have a 200 amp service (meter base)feeding a 100A main and a 100A subpanel (disconnect) which feeds my 100A main at my shop.

I was told this was no longer allowed by the NEC. The shop would have to be supplied by a breaker from the house Main or one Sub panel (disconnect) that supplies the house main and the Shop main.

Just curious as I want my set up to meet NEC code.

Thanks
Mark
 
Last edited:
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
who told you this and did they cite a code section?
 
OP
M

mkbrower

Active member
Joined
Aug 11, 2010
Messages
44
Location
Foot Hills of North Carolina
A few co-workers who has done electrical DIY work. No code recited but was told I could not find a meter base now that would allow multiple feeds without an attached sub panel.

Mark
 
To avoid these ads, REGISTER NOW!
OP
M

mkbrower

Active member
Joined
Aug 11, 2010
Messages
44
Location
Foot Hills of North Carolina
I have only one subpanel (disconnect) feeding off the meter base before going to the shop. The house main panel is also being fed from the meter with no disconnect. Local code does require disconnects for AC/shop etc but I was told the disconnects MUST be fed from the Main panel.

Mark
 
Last edited:

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
230.40 exception #3: a single family dwelling unit and a seperate structure shall be permitted to have one set of service entrance conductors run to each from a single service drop or latteral.what do you think?
 