Ok so first let me apologize. I know there are a million threads on this. This is my first ever post on any type of forum so I'm not really sure of posting "rules" when it comes to when it's appropriate to start a new thread
Now for my question and I'll be as specific as I can.
I bought a house with a detached garage. The garage is wired with a 14 gauge romex type wire (white shielding, more round than flat) for basic spiral cfl lights and outlets. From the looks of things, someone ran 10 gauge wire from the house to the garage into a fuse box. The wire was ran overhead and, while the house was vacant, someone cut the wire for scrap I assume. I have a little higher demand from my garage than it is wired for right now.
I have 150 amp service to my house and the breaker that was originally used for the garage run is 40 amp. Giving myself a few (about 8) extra feet of wire, I'll need about 125 feet of wire to run to the garage. I have a 50 amp stick welder that I've used maybe 3 times in the last decade and I want to go to a medium sized compressor (maybe 25 amps) as the one I have now is a little too small but only draws 15 amps.
I have a sub that's rated 50 amps so I am assuming I need a new, larger sub or I need to do away with the welder. I also want to run a router extender for wi-fi in the garage as well as, maybe, cable for a tv and possibly a phone. My phone now runs off my cable router so I may not have to run a wire for that.
So, finally the questions are:
What size sub? What size breaker in the main and what size wire should I run considering the load drop over the 125 ft? I want to bury it and I prefer copper as I don't want to worry about the aluminum oxidizing or becoming loose. I'd like to run 240 in the garage also. How deep do I bury it? Can I run all the low voltage stuff in one conduit? Do I need a designated ground rod for the garage? More than one? How far apart and what size? I live in north-east Ohio. Should I run the copper in conduit or, if I get the water rated stuff, is it better to bury it without? I believe conduit is mandatory where the wire enters and leaves the ground. How deep does the conduit have to be in those areas?
I know it's a ton of info/questions and I'm sure I still missed some info. Your patience and answers are appreciated.
Mark
Now for my question and I'll be as specific as I can.
I bought a house with a detached garage. The garage is wired with a 14 gauge romex type wire (white shielding, more round than flat) for basic spiral cfl lights and outlets. From the looks of things, someone ran 10 gauge wire from the house to the garage into a fuse box. The wire was ran overhead and, while the house was vacant, someone cut the wire for scrap I assume. I have a little higher demand from my garage than it is wired for right now.
I have 150 amp service to my house and the breaker that was originally used for the garage run is 40 amp. Giving myself a few (about 8) extra feet of wire, I'll need about 125 feet of wire to run to the garage. I have a 50 amp stick welder that I've used maybe 3 times in the last decade and I want to go to a medium sized compressor (maybe 25 amps) as the one I have now is a little too small but only draws 15 amps.
I have a sub that's rated 50 amps so I am assuming I need a new, larger sub or I need to do away with the welder. I also want to run a router extender for wi-fi in the garage as well as, maybe, cable for a tv and possibly a phone. My phone now runs off my cable router so I may not have to run a wire for that.
So, finally the questions are:
What size sub? What size breaker in the main and what size wire should I run considering the load drop over the 125 ft? I want to bury it and I prefer copper as I don't want to worry about the aluminum oxidizing or becoming loose. I'd like to run 240 in the garage also. How deep do I bury it? Can I run all the low voltage stuff in one conduit? Do I need a designated ground rod for the garage? More than one? How far apart and what size? I live in north-east Ohio. Should I run the copper in conduit or, if I get the water rated stuff, is it better to bury it without? I believe conduit is mandatory where the wire enters and leaves the ground. How deep does the conduit have to be in those areas?
I know it's a ton of info/questions and I'm sure I still missed some info. Your patience and answers are appreciated.
Mark
Where do people come up with this stuff! I think grounding has got to be the most confusing thing for people to grasp as evidenced above!