Since I will be adding a new plasma cutter and a new MIG welder to my existing TIG welder I have decided to replace my welder outlet with a sub-panel and add multiple outlets. I currently have a 1.25" EMT conduit with a about a 55' run to my welder. Since I already have the 1.25" conduit I would like to max it out with #1 AGW wire to get 125 amp capacity to the sub panel.
Technically 4 #1' really don't fit in a 1.25" conduit depending on how you round. but 3#1 and a #2 will fit. Also I'm I correct in assuming that I could reduce both the ground and neutral 2 wire sizes and use 2 #1 and 2 #3? That would save alot of money and ease the pull.
As far as the sub panel goes do I need to get one with a main breaker or do they make them without and if the main breaker is required is there a sub panel available with a 125 amp main breaker.