quickfarms
Well-known member
I want to add a sub panel in my yard halfway between my main panel and the shop sub panel
The goal is to add a 50 amp RV power box for now and eventually convert it to a sub panel for a future building
My research has lead me to believe that the electrical code has changed since I built the existing shop 18 years ago
When the existing sub panel was installed we ran two empty 3/4” pvc conduits in the trench
Based on the old code I could pull 3 #8 thhn wires and use a ground rod like the sub panel.
Now I think I need to also pull a ground, is this correct?
If I add a third conductor to the conduit I would need to pull #6 for 50 amps or use a 40 amp breaker due to the 80% derating
First question is does the ground need to be the same size or can I use a #10 wire?
Can you actually pull this through the 3/4” pvc conduit?
What is the best way to hook up the wire to the fish tape for pulling?
Do I still need to install a ground rod?
The goal is to add a 50 amp RV power box for now and eventually convert it to a sub panel for a future building
My research has lead me to believe that the electrical code has changed since I built the existing shop 18 years ago
When the existing sub panel was installed we ran two empty 3/4” pvc conduits in the trench
Based on the old code I could pull 3 #8 thhn wires and use a ground rod like the sub panel.
Now I think I need to also pull a ground, is this correct?
If I add a third conductor to the conduit I would need to pull #6 for 50 amps or use a 40 amp breaker due to the 80% derating
First question is does the ground need to be the same size or can I use a #10 wire?
Can you actually pull this through the 3/4” pvc conduit?
What is the best way to hook up the wire to the fish tape for pulling?
Do I still need to install a ground rod?