Sub panel read making me question my house service

Wrigley

Active member
Joined
Dec 1, 2017
Messages
41
Location
SE IA
I have decided it is time to finish my detached garage. It has been an unheated shell for a few years now. Currently one light and one electrical plug. I had felt pretty confident in my wiring abilities but before finishing the wiring and covering things up with insulation and drywall I decided to do a little reading here. Now I am concerned, not with the detached garage but with my house panel. I built the house starting in 2006. Electric service was first thing I put in so I could have temporary power to build the house. I have underground into a big green box that feeds a meter and a 200 amp disconnect that are probably 75 feet from the house and attached to a treated lumber stand. The disconnect has bond neutral to ground here with a couple of ground rods. I then run underground with 2 hots and the neutral no bare ground to the house with direct burial alluminum, into 2 inch pvc under attached garage slab to a 200 amp 40 space square d qo panel. This panel has bonded neutral and ground and has been fixed to ground rods outside the house. Reading a few spots here I am now thinking I should have had a 4th bare ground running with my three wire and the panel Unbonded. I can also find examples where this is acceptable and expected on other forums. I am now questioning my house panel setup!!! The feed for the unattached garage is a four wire 100 amp qo 12 space box I installed back in or around 2010. It’s is not bonded with enclosure,aluminum wire run underground in pvc unbonded with machine grounds separated and attached to a ground rod outside of the building. I should also mention I did the work with an electrician friend guiding me and live in rural Iowa. Is the bonding of my house panel correct?
 
Last edited:
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I can't remember offhand what code cycle it changed but three wire feeders were okay once upon a time. Today you need four wire feeders after the first disconnect. So today if your service was done you'd have three wire from meter to that 200A disconnect and from there to every other panel it would be four wire.
 
OP
W

Wrigley

Active member
Joined
Dec 1, 2017
Messages
41
Location
SE IA
Thanks pattenp for the response. My bigger concern is if the house panel should be bonded? I am getting conflicting thoughts about that portion.
 