Hi everyone,
The building & electrical inspectors just visited my detached garage and the electrical inspector advised me that I've miswired the subpanel and created a ground-loop. This was a huge surprise. Would you guys mind reading through my setup and tell me what I did wrong, because he declined to clarify why the circuit is flawed and although I will make the change he requested, I really want to understand why this is incorrect.
- The subpanel is supplied by 3, #3 RW90 lines (no issues with those) from the main panel in the house.
- The subpanel's neutral bus is not bonded to its ground bus.
- There are 2, 10' long, 3/4" copper grounding rods (driven a few inches below grade) connected by a contiguous 6awg bare ground wire which then connects to the subpanel's ground bus.
Specifically, the inspector said "those rods are useless" and that I should have ran a single insulated ground line to the panel and he repeated a few times that I'd created a ground loop. But I cannot for the life of me see it - I mean, I will pull the 4th line as per his request, but I don't understand why.
Any info is much appreciated!
The building & electrical inspectors just visited my detached garage and the electrical inspector advised me that I've miswired the subpanel and created a ground-loop. This was a huge surprise. Would you guys mind reading through my setup and tell me what I did wrong, because he declined to clarify why the circuit is flawed and although I will make the change he requested, I really want to understand why this is incorrect.
- The subpanel is supplied by 3, #3 RW90 lines (no issues with those) from the main panel in the house.
- The subpanel's neutral bus is not bonded to its ground bus.
- There are 2, 10' long, 3/4" copper grounding rods (driven a few inches below grade) connected by a contiguous 6awg bare ground wire which then connects to the subpanel's ground bus.
Specifically, the inspector said "those rods are useless" and that I should have ran a single insulated ground line to the panel and he repeated a few times that I'd created a ground loop. But I cannot for the life of me see it - I mean, I will pull the 4th line as per his request, but I don't understand why.
Any info is much appreciated!