This is a two part question. Thanks for bearing with me!
1)
105 ft of 1-1/4" conduit is installed from main service panel to 100amp sub panel.
Planned on an 80 amp breaker and #4 copper THHN to feed the sub panel.
This is a small 240 sqft shop, and it is very rare that more than one power tool will be used at a time.
I recently decided to go with electric resistance over natural gas for heat, for this year anyway. I am in the south and the shop is well sealed and insulated so the load is small and infrequent. The payback wasn't there for nat gas.
I need a sanity check. Due to "more is better" I am second guessing my 80 amp service.
Concurrent (not continuous) loads-
Lighting 6 amps 120v
Heater 11-20 amps 240v
Compressor 20 amps 120v
Intermittant loads (select any one to add to above list)
Welder 20 amps
Plasma 22 amps
saw/grinder etc ~12
If I add all the concurrent loads I am at 46 amps when the compressor is starting. This leaves 34 amps for any single tool to be operating when compressor starts.
I think this means I am good with 80 amps. I just don't really want the lights dimming when the compressor cuts on while I am plasma cutting etc.
Part 2)
An electrician friend of mine suggested aluminum to keep costs down. I don't much care for aluminum in a residential setting except for SER, but cutting wire cost by 60% is pretty attractive. What would you do? I'm also a little concerned about the 3 #2 Al conductors and a ground being difficult to pull. I have pull boxes every 360 degrees per code but still concerned.
1)
105 ft of 1-1/4" conduit is installed from main service panel to 100amp sub panel.
Planned on an 80 amp breaker and #4 copper THHN to feed the sub panel.
This is a small 240 sqft shop, and it is very rare that more than one power tool will be used at a time.
I recently decided to go with electric resistance over natural gas for heat, for this year anyway. I am in the south and the shop is well sealed and insulated so the load is small and infrequent. The payback wasn't there for nat gas.
I need a sanity check. Due to "more is better" I am second guessing my 80 amp service.
Concurrent (not continuous) loads-
Lighting 6 amps 120v
Heater 11-20 amps 240v
Compressor 20 amps 120v
Intermittant loads (select any one to add to above list)
Welder 20 amps
Plasma 22 amps
saw/grinder etc ~12
If I add all the concurrent loads I am at 46 amps when the compressor is starting. This leaves 34 amps for any single tool to be operating when compressor starts.
I think this means I am good with 80 amps. I just don't really want the lights dimming when the compressor cuts on while I am plasma cutting etc.
Part 2)
An electrician friend of mine suggested aluminum to keep costs down. I don't much care for aluminum in a residential setting except for SER, but cutting wire cost by 60% is pretty attractive. What would you do? I'm also a little concerned about the 3 #2 Al conductors and a ground being difficult to pull. I have pull boxes every 360 degrees per code but still concerned.