Sub panel

Jking24

Well-known member
Joined
Feb 27, 2018
Messages
258
I know this has been covered many times but I'm having trouble using the search menu with my phone after a update. So I'm just gonna ask im planing to put either a 75 or 100 amp sub panel in the far corner of my garage. It's about 115-120ft run breaker to breaker. I know that i need three conductor and that i need to separate or i believe "float" the ground from the neutral Two questions what size aluminum would i need for each option and is ser cable allowed to be used in this application ? If not what should be used. Thanks in advance
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
SER can be used. 2-2-2-4 AL for up to 90A or 1-1-1-3 AL for up to 100A. There is no 75A breaker.
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,749
Location
NW Iowa
Attached? If so SER is great. Needs 4 wires total, 2 hots, neutral and ground. SER has all 4
 
OP
J

Jking24

Well-known member
Joined
Feb 27, 2018
Messages
258
Attached? If so SER is great. Needs 4 wires total, 2 hots, neutral and ground. SER has all 4

The garage is detached but this will be from the main 200 amp panel to the opposite inside corner. Just to ber clear ser could be run with no conduit correct ?
 
OP
J

Jking24

Well-known member
Joined
Feb 27, 2018
Messages
258
SER can be used. 2-2-2-4 AL for up to 90A or 1-1-1-3 AL for up to 100A. There is no 75A breaker.

Thankyou for the info i knew their isnt a 75 my mind is just a little scattered right now lol
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,749
Location
NW Iowa
The garage is detached but this will be from the main 200 amp panel to the opposite inside corner. Just to ber clear ser could be run with no conduit correct ?

If the run goes underground then ser will not be an option at least for that portion. Ser can be run outdoors but never underground even in a conduit.
 
OP
J

Jking24

Well-known member
Joined
Feb 27, 2018
Messages
258
If the run goes underground then ser will not be an option at least for that portion. Ser can be run outdoors but never underground even in a conduit.

Entire run will be inside leaving main panel going up inside of wall across rafters then down the other wall into sub panel
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,749
Location
NW Iowa
Entire run will be inside leaving main panel going up inside of wall across rafters then down the other wall into sub panel

Got it. Service panel is already in the garage. Ser is a good choice. No conduit needed it installs like Romex for the most part.
 

78SC4X4

Well-known member
Joined
Apr 21, 2018
Messages
370
Location
Port Orchard Wa
I know this has been covered many times but I'm having trouble using the search menu with my phone after a update. So I'm just gonna ask im planing to put either a 75 or 100 amp sub panel in the far corner of my garage. It's about 115-120ft run breaker to breaker. I know that i need three conductor and that i need to separate or i believe "float" the ground from the neutral Two questions what size aluminum would i need for each option and is ser cable allowed to be used in this application ? If not what should be used. Thanks in advance

In case you haven't seen it, post 3 of the Electrical FAQ sticky shows the diagram of what you are describing.

https://www.garagejournal.com/forum/showthread.php?t=356460
 
OP
J

Jking24

Well-known member
Joined
Feb 27, 2018
Messages
258
Sounds good thanks bert and yes i have seen the sticky 4x4 lots of good info on that one
 