Hello everyone,
Looking to confirm/adjust my minimum wiring configuration for a subpanel (100 amp). The subpanel will be located in a detached garage and the wires will travel from the main to the subpanel via a pvc conduit (1 1/4) underground. The total distance is 40 feet or less. Beside unbounding/isolating the neutral bar and adding two ground rods, is the following configuration correct?
* Wires protected by 80 amp breaker at the main
* #4 cu for black
* #4 cu for red
* #4 cu for white
* #8 cu for ground/green
Do I need to step up to #3 cu for the 80 amp breaker? Does the #8 cu for the green wire meet the minimum requirements? Am I missing anything else?
Thank you.
Looking to confirm/adjust my minimum wiring configuration for a subpanel (100 amp). The subpanel will be located in a detached garage and the wires will travel from the main to the subpanel via a pvc conduit (1 1/4) underground. The total distance is 40 feet or less. Beside unbounding/isolating the neutral bar and adding two ground rods, is the following configuration correct?