Please tell me anything at all thats not right
EDIT: Flipped and attached the original picture.. ..Eric
What size wire is that? And what is feeding it? That wire seems undersized for 100A.
Looks like #6 UF-B...And the breaker in the sub is a disconnect only. What matters is the size of the breaker in the upstream panel...
Panel looks good, isolated neutral, check....
Is this a detached structure?
C96
I am going to assume that the bare copper wire connected to the bonded ground bar and exiting through the small hole in the back of the panel is #8 and is connected to a ground rod, or approved grounding electrode.
If my assumptions are correct, then your install should be fine regarding the grounding and bonding for the 100a rating of the panel.
As Wylie mentioned, the main breaker in this panel is only meant for a disconnecting means. However, the breaker supplying this feeder must not exceed the allowable rating for the feeder conductors used in this application.
Also, the feeder must be sized and appropriate for the load served.
Nice job! :thumbup:
Beemer533
Syracuse, NY
Yes, I should have phrased my question more specifically ; when I asked "what was feeding it", I meant the downstream breaker.
This post edited by the NSA
23 CHIEF
Buffalo NY
I don't think it has a lock tab but it is locked down with a screw that the way it was new do I need a lock tab
Norcal
Where is the lock tab for that breaker so you can't use the spot across from it?
The bus stabs are notched at the factory, so the spaces adjacent to the main are unusable.
To the OP: The breaker has a screw to fasten the main, your fine.
flyboy1100
I see that now. The panel I used didn't have that so o had a screw in lock tab that also prevented use of the opposing side.
23 CHIEF
Buffalo NY
Thanks everybody for dubble checking this to make sure it is right.I got all the info on how to correctly complete this from theads on this forum. This group of people have helped for ideas and projects I never would of even thought of taking on. So thanks again.
23 CHIEF
Buffalo NY
Yeah
EDIT: flipped and attached picture. . . . Eric
C96
Chief, I can see you take a great deal of pride in what you do…:beer:
I must say, your work is picture perfect, definitely done in a nice workman like manner. Everything is neat, plumb, level, and clean, a job well done with a considerable amount of love thrown in…Lol.
Sad to say, but this is much nicer than many professional jobs I’ve run across.
This is a good example of how to install a simple basic residential sub panel in a detached structure. :thumbup:
23 CHIEF
Buffalo NY
Chief, I can see you take a great deal of pride in what you do…[emoji481]
This is a good example of how to install a simple basic residential sub panel in a detached structure. [emoji106]
Thank you
:+1: to all of that.
Its unbelievable sometimes the work Ive seen that was done by "LICENSED professionals".... :wtf: