What size wire is that? And what is feeding it? That wire seems undersized for 100A.
Yes, I should have phrased my question more specifically ; when I asked "what was feeding it", I meant the downstream breaker.Looks like #6 UF-B...And the breaker in the sub is a disconnect only. What matters is the size of the breaker in the upstream panel...
Panel looks good, isolated neutral, check....
Is this a detached structure?
Where is the lock tab for that breaker so you can't use the spot across from it?![]()
Please tell me anything at all thats not right
Where is the lock tab for that breaker so you can't use the spot across from it?
Is there not a ground going back to the main panel?
I see that now. The panel I used didn't have that so o had a screw in lock tab that also prevented use of the opposing side.The bus stabs are notched at the factory, so the spaces adjacent to the main are unusable.
To the OP: The breaker has a screw to fasten the main, your fine.
Ah I see it now.There is,it's one of the two ground wires you see on the bar

Yeah the pic is sideways sorry
Thank youChief, I can see you take a great deal of pride in what you do…[emoji481]
I must say, your work is picture perfect, definitely done in a nice workman like manner. Everything is neat, plumb, level, and clean, a job well done with a considerable amount of love thrown in…Lol.
Sad to say, but this is much nicer than many professional jobs I’ve run across.
This is a good example of how to install a simple basic residential sub panel in a detached structure. [emoji106]
Chief, I can see you take a great deal of pride in what you do…
I must say, your work is picture perfect, definitely done in a nice workman like manner. Everything is neat, plumb, level, and clean, a job well done with a considerable amount of love thrown in…Lol.
Sad to say, but this is much nicer than many professional jobs I’ve run across.
This is a good example of how to install a simple basic residential sub panel in a detached structure.![]()
to all of that.