2 Mini Split AC units are 9K BTU units, they are 240V, the min. circuit amplicity is 10 or 12A each and Max COP / Fuse is 15A each.
The AC units Rated input is around 800-1000W max so at 240V is only a few amps.
I was thinking instead of running 4 conductor THHN wires in conduit to the locations or maybe I could put in an outdoor rated subpanel.
so questions
1) I think the ones I saw is 60 amp and 4 space, however can you suggest (if) I can use a smaller feeding breaker like 30A on those load centers?
2) I have to run neutral even of I am not going to be using it?
2b) Do I need to run ground wire or can use EMT as the EGC in this?
The AC units Rated input is around 800-1000W max so at 240V is only a few amps.
I was thinking instead of running 4 conductor THHN wires in conduit to the locations or maybe I could put in an outdoor rated subpanel.
so questions
1) I think the ones I saw is 60 amp and 4 space, however can you suggest (if) I can use a smaller feeding breaker like 30A on those load centers?
2) I have to run neutral even of I am not going to be using it?
2b) Do I need to run ground wire or can use EMT as the EGC in this?
lights and power tools too