Hello,
Looking for some input on wiring my attached garage with a subpanel.
I have a newish house that was built (by others) with little room for expansion in mind. It has a 16 space main panel and most of the house runs off of a 125A sub panel from there. The main is filled with most of the 2 pole circuits and a generator interlock breaker. The good news is I have a 200A service so I am fine on power but short on free space in panels.
The 125A panel (closer to shop) is loaded up with the maximum tandems (only bottom 5 allowed) except for two spaces. While physically possible to install 2 more tandems and gain 2 spaces I don't view that as a good option for wiring a sub panel for my shop.
So I am planning to run about 120 feet in the attic all the way back to the main for the shop sub panel which only has two spaces free.
Loads in the shop will be a 1 or 2 stage compressor (3-5 HP). I'll also need a 2 pole space for a future mini split. I'm OK on receptacles/lighting for now with what exists.
Which brings me to my question. What wire would you run?
6/3 with ground for a 60 amp subpanel would work but might be pushing the limits on voltage drop for that length.
For the same money I can run 2-2-2-4 Aluminum and probably have 90 amp capacity for future use. I suspect the thicker aluminum will be as easy to run as the thinner copper.
I can't see myself using 90 amps but I sure as heck don't want to run through the attic to the main again at a later date.
Seems to me like the AL is the way to go. Any caveats to using the AL conductor in this application? Anything special to terminate to the panels or breakers?
Apologies for the longwinded post.
Looking for some input on wiring my attached garage with a subpanel.
I have a newish house that was built (by others) with little room for expansion in mind. It has a 16 space main panel and most of the house runs off of a 125A sub panel from there. The main is filled with most of the 2 pole circuits and a generator interlock breaker. The good news is I have a 200A service so I am fine on power but short on free space in panels.
The 125A panel (closer to shop) is loaded up with the maximum tandems (only bottom 5 allowed) except for two spaces. While physically possible to install 2 more tandems and gain 2 spaces I don't view that as a good option for wiring a sub panel for my shop.
So I am planning to run about 120 feet in the attic all the way back to the main for the shop sub panel which only has two spaces free.
Loads in the shop will be a 1 or 2 stage compressor (3-5 HP). I'll also need a 2 pole space for a future mini split. I'm OK on receptacles/lighting for now with what exists.
Which brings me to my question. What wire would you run?
6/3 with ground for a 60 amp subpanel would work but might be pushing the limits on voltage drop for that length.
For the same money I can run 2-2-2-4 Aluminum and probably have 90 amp capacity for future use. I suspect the thicker aluminum will be as easy to run as the thinner copper.
I can't see myself using 90 amps but I sure as heck don't want to run through the attic to the main again at a later date.
Seems to me like the AL is the way to go. Any caveats to using the AL conductor in this application? Anything special to terminate to the panels or breakers?
Apologies for the longwinded post.