I'm considering adding a subpanel to my house (mainly for garage use).
I have a 3/2 house with drive-under garage like is so common in this area. It has 150A service to a 24-space Cutler-Hammer panel for the following major loads:
50A breaker for range (I may swap this to a gas unit, but would like to leave the range circuit intact)
30A breaker for dryer
30A breaker for A/C
30A breaker for 3hp air compressor
The rest is 15A/20A 120v general purpose receptacles / lighting and such.
As is, I had to combine two circuits to have room for the compressor. I would like to separate those two combined circuits, as well as allow room for expansion (might want 240v for something else in the future).
Panel brand... I had intended to stick with Cutler-Hammer (or, Eaton CH series as it's apparently called now). Any reason not to? Any reason to just replace the whole thing with a panel including more spaces instead of adding a subpanel?
Assuming I go with the subpanel... where do I put it?
1. Next to the existing panel. Install is easier. I will move 2-3 circuits to the subpanel, those would be easier as well.
2. In the garage where future expansion will be easier (I suspect most future circuits will be run to locations in the garage).
Last, type of installation...
1. Flush mount panel. I'd definitely use this if installed next to the existing one (flush mount in a finished wall). If in the garage, I'd have to pick a section of frame wall for it.
2. Surface mount panel. This would work if I chose to install it over a concrete block section of wall - but then I guess I also need to run conduit up to the joists above where NM cable will be run. How do you handle the entrance into the conduit, a large JB with cables clamped at the entrance to the JB?
I have a 3/2 house with drive-under garage like is so common in this area. It has 150A service to a 24-space Cutler-Hammer panel for the following major loads:
50A breaker for range (I may swap this to a gas unit, but would like to leave the range circuit intact)
30A breaker for dryer
30A breaker for A/C
30A breaker for 3hp air compressor
The rest is 15A/20A 120v general purpose receptacles / lighting and such.
As is, I had to combine two circuits to have room for the compressor. I would like to separate those two combined circuits, as well as allow room for expansion (might want 240v for something else in the future).
Panel brand... I had intended to stick with Cutler-Hammer (or, Eaton CH series as it's apparently called now). Any reason not to? Any reason to just replace the whole thing with a panel including more spaces instead of adding a subpanel?
Assuming I go with the subpanel... where do I put it?
1. Next to the existing panel. Install is easier. I will move 2-3 circuits to the subpanel, those would be easier as well.
2. In the garage where future expansion will be easier (I suspect most future circuits will be run to locations in the garage).
Last, type of installation...
1. Flush mount panel. I'd definitely use this if installed next to the existing one (flush mount in a finished wall). If in the garage, I'd have to pick a section of frame wall for it.
2. Surface mount panel. This would work if I chose to install it over a concrete block section of wall - but then I guess I also need to run conduit up to the joists above where NM cable will be run. How do you handle the entrance into the conduit, a large JB with cables clamped at the entrance to the JB?