Hello,I built a detached structure. I am planning on running a 100 amp line from the main. A friend gave me a 200 amp full panel today use,lots of connections. My question is do I have too change the main breaker on panel to match the feed?

Thanks you for any and all help..

Dan
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
No you dont need to change the main in the subpanel.

It will just act as a disconnect.

The breaker in the feeding panel will serve as the overcurrent protection.

Make sure to isolate the neutral bar in the subpanel.

You may need a ground bar kit.

Also the feed needs to be 4-wire and dont forget 2 ground rods
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
No you dont need to change the main in the subpanel.

It will just act as a disconnect.

The breaker in the feeding panel will serve as the overcurrent protection.

Make sure to isolate the neutral bar in the subpanel.

You may need a ground bar kit.

Also the feed needs to be 4-wire and dont forget 2 ground rods
::thumbup::thumbup::thumbup::thumbup:
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
No you dont need to change the main in the subpanel.

It will just act as a disconnect.

The breaker in the feeding panel will serve as the overcurrent protection.

Make sure to isolate the neutral bar in the subpanel.

You may need a ground bar kit.

Also the feed needs to be 4-wire and dont forget 2 ground rods

What ^^ he ^^ said.


What kind of wire were you going to run? Conduit? If so....make sure it's rated THWN (wet locations).

Don't be afraid to up size it. Makes for an easier pull.

You might also want to consider a second conduit for data.
My garage is detached and behind my house. I actually have my internet cable going to the garage and then through conduit to my house. Saves me having the cable hanging above my yard.
 

TTnicksocal

Member
Joined
Jul 24, 2018
Messages
9
Location
San Bernardino
No you dont need to change the main in the subpanel.

It will just act as a disconnect.

The breaker in the feeding panel will serve as the overcurrent protection.

Make sure to isolate the neutral bar in the subpanel.

You may need a ground bar kit.

Also the feed needs to be 4-wire and dont forget 2 ground rods


Dont want to Hyjack the but i am doing this exact thing. New detached garage 200 Amp service on the home and installed a 100amp sub panel in the new garage.

I went with 6-3 cable for the feed to the garage. My question is on my panel these are two spots to put the ground. There is a bar that is grounded to the panel and there is another which is not grounded (sitting up on top of a plastic insulator). My 6-3 came with 4 wires. two hots a size, a 6ga neutral/ground and a bare 12-14ga wire.

Does the 6ga neutral/ground go to the insulated ground or the "grounded" bar? and Does the bare wire go on the grounded or insulated grounding bar?
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
We get where explained where a lot but not why. In this case some why will help with where. Feel free to jump in as I am not always clear.
So,,, the goal here is to keep all the neutrals in a second panel insulated. Note the white wire is coated. Insulation g them keeps all the operating currents on the wire they are intended to and not exposed to the frames and chassis of equipment.
The ground wire, green or bare is hooked to all the exposed.metal that has the potential to become energized at the same potential,,, think spider Web with all tied together and providing a low impedence, low resistance pathway back to its source, neutral at service main which allows the current to trip the breaker in the event of a fault,, or short circuit. By being grounded in this web there is no difference between any 2 pieces of grounded equipment including the panel enclosures.
Now the rods. They are tied to the equipment ground, anything connected to.them would be grounded and along with their primary purpose of carrying lightening and static to earth they reduce some of the step potential between equipment and the ground, concrete you are standing on. The idea of caring strikes there is to reduce the chance it is carried back to the main thru the ground wire.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Dont want to Hyjack the but i am doing this exact thing. New detached garage 200 Amp service on the home and installed a 100amp sub panel in the new garage.
I went with 6-3 cable for the feed to the garage.

6-3 UF cable is only rated for 55A, and you have a 100A breaker?
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
So,, all the bare or green wires connected to the ground bar in a sub including rods, in the main all connected to grounded bonded neutral. Doesn't mean you can't have an extra bar in a main, often used to reduce congestion but it must be bonded to neutral.
 
To avoid these ads, REGISTER NOW!

TTnicksocal

Member
Joined
Jul 24, 2018
Messages
9
Location
San Bernardino
6-3 UF cable is only rated for 55A, and you have a 100A breaker?

Yes the panel is 100amps rated but im only going to be runnning a 60amp breaker at the main panel. If i start popping it i'll pull two more 2ga or 4ga wires and beef it up a bit.

55amps is alot... All im planning on running is;
200amp Welder
Plasma cutter
air compressor
handheld grinders
LED fluorescent style lighting

its sounds like a lot but i am a one man show and it will be rare for a few of those things running at the same time.

When i first got my Syncrowave it was running off a 50amp breaker fed by 12ga romex in the garage and never once popped the breaker.
 
Last edited:

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
Hello,I built a detached structure. I am planning on running a 100 amp line from the main. A friend gave me a 200 amp full panel today use,lots of connections. My question is do I have too change the main breaker on panel to match the feed?



Thanks you for any and all help..



Dan
Is the 200 amp panel new or used? What brand and style? Used can be ok but there are some brands or styles of a brand that aren't worth the time to install even if free.

Sent from my SM-G965U using Tapatalk
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Yes the panel is 100amps rated but im only going to be runnning a 60amp breaker at the main panel. If i start popping it i'll pull two more 2ga or 4ga wires and beef it up a bit.

You can't parallel wires smaller than 1/0. And even then, the wires must all be the same gauge and type.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,375
Location
Richmond, VA
Yes the panel is 100amps rated but im only going to be runnning a 60amp breaker at the main panel. If i start popping it i'll pull two more 2ga or 4ga wires and beef it up a bit.

55amps is alot... All im planning on running is;
200amp Welder
Plasma cutter
air compressor
handheld grinders
LED fluorescent style lighting

its sounds like a lot but i am a one man show and it will be rare for a few of those things running at the same time.

When i first got my Syncrowave it was running off a 50amp breaker fed by 12ga romex in the garage and never once popped the breaker.

Hopefully you didn't run 6/3 NM-B...
 

4x4Petr

Member
Joined
Mar 30, 2019
Messages
18
Location
Innisfil ON
I ran three pvc to garage, one for the electrical, one for ethernet cameras etc, and one for a gas line..

You might find that the one for the gas line doesn't get used. I am a gas fitter and generally prefer to go direct burial and not through a conduit with gas piping to detached structures. Mainly because I know it won't be damaged by someone in the future trying to feed something else in with the gas pipe. It may not be that easy to feed a gas line through a pvc conduit unless it's a completely straight run. Plastic underground gas piping has termination ends that bend from underground to above usually at the point of entry in a building. If you were to install it through a pvc conduit you either cannot have the termination ends or have to use some other termination type for the plastic. Your gas fitter will have the ultimate decision. But conduits are like tools- it's better to have a spare and not need it than to need one and not have it:)
 