I'm running a subpanel under the supervision of my father in law (licensed electrician). I've never run a subpanel before, so I'm taking my time, and asking questions as I go along to whomever will listen!
I've got the subpanel up, but am a bit baffled by the mounting location Eaton put for the ground bar. It's literally on the side of the panel, not on the backplate, so basically once breakers are in you're either using a 90* or stubby flathead to tighten. Now, I don't intend to run any more circuits, so the possibility of this being annoying down the road is small, but I'm wondering if should get a different panel with a more reasonable ground bar mount anyway.
The panel I've currently got: Eaton CH8L125SP
The 12 space model looks a lot better to me:
EATON SCH12L125BP
Lastly, I've currently got the panel secured with two screws into a stud. If I remember right, I believe the code intends for surface mount panels to be secured in all 4 corners, but there aren't corner mounting holes on this 8 space panel. If I keep it, is how I have it mounted satisfactory? Again, the 12 space looks like it is designed better in this area as well.
Does anyone have any thoughts on the ground bar and mounting concerns?
Thanks!
Karson
I've got the subpanel up, but am a bit baffled by the mounting location Eaton put for the ground bar. It's literally on the side of the panel, not on the backplate, so basically once breakers are in you're either using a 90* or stubby flathead to tighten. Now, I don't intend to run any more circuits, so the possibility of this being annoying down the road is small, but I'm wondering if should get a different panel with a more reasonable ground bar mount anyway.
The panel I've currently got: Eaton CH8L125SP
The 12 space model looks a lot better to me:
EATON SCH12L125BP
Lastly, I've currently got the panel secured with two screws into a stud. If I remember right, I believe the code intends for surface mount panels to be secured in all 4 corners, but there aren't corner mounting holes on this 8 space panel. If I keep it, is how I have it mounted satisfactory? Again, the 12 space looks like it is designed better in this area as well.
Does anyone have any thoughts on the ground bar and mounting concerns?
Thanks!
Karson