Subpanel off of a subpanel

bxkubota

Member
Joined
Mar 27, 2012
Messages
8
I have a 200 amp panel in my house and all the spaces for breakers a taken. I have a 100 amp breaker with aluminum wire running to a 100 amp subpanel on the back of my house for my hot tub. My question is can I run another subpanel off of this subpanel for my garage that is about 60 feet away. I have open spaces in the 100 amp subpanel that services my hot tub.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Sure you can but you need to be mindful of the loads you may have in the garage as to not over load the 100A sub-panel.
 

SiGmA_X

Well-known member
Joined
Aug 13, 2005
Messages
1,111
Location
Portland, OR
Patten, would he need to worry about additional voltage drop for the first subpanel, too? Because effectively, if the hottub is 100ft from the main panel, and the garage 100ft from the hottub sub, he's looking at 200ft?

Thanks for the info!
 
OP
B

bxkubota

Member
Joined
Mar 27, 2012
Messages
8
The hot tub is about 50 feet from the main panel with AA-8030 aluminum wire going to the hot tub sub panel. If someone could give me an idea what wire to run to from the hot tub panel to the garage subpanel and the size of the subpanel that would work in the garage.
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
B

bxkubota

Member
Joined
Mar 27, 2012
Messages
8
Patten, would he need to worry about additional voltage drop for the first subpanel, too? Because effectively, if the hottub is 100ft from the main panel, and the garage 100ft from the hottub sub, he's looking at 200ft?

Thanks for the info!

The total distance from my main panel to the new garage sub panel is around 110 ft give or take.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Yes distance and size of the feed also need to be considered because of voltage drop. I'd say in most cases if the total run is under 200 ft then VD may not be a big issue but that's not to say it can't be an issue.

Patten, would he need to worry about additional voltage drop for the first subpanel, too? Because effectively, if the hottub is 100ft from the main panel, and the garage 100ft from the hottub sub, he's looking at 200ft?

Thanks for the info!
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I would still come off the main panel, even if the hot tub panel was closer. Unless it was impossible. They make twins/quads to free up spaces. But no way of knowing if it'll work for you without looking at your panel.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Are you in the US? Need to know what size AL wire is feeding the existing hot tub sub-panel? The AA-8030 is the aluminum alloy type. What's the AWG? Also, how many conductors are feeding the sup-panel, 3 or 4?

The hot tub is about 50 feet from the main panel with AA-8030 aluminum wire going to the hot tub sub panel. If someone could give me an idea what wire to run to from the hot tub panel to the garage subpanel and the size of the subpanel that would work in the garage.
 