Subpanel or new service?
catldavis
Hello all, trying to figure out how to power my shop. My house has a 200 amp panel. All of the spaces in the box have breakers except for two. Therefore, I could put a double-pole 100 amp breaker in the panel. However, I have a significant run to the shop, better than 350 ft so I'm concerned what size wire it will take not to have too much drop. Any idea how to size the wire?
My other option is to see if the power company will allow another main from the power pole. The problem with this is the cost to make it happen. Additionally, the power company has a healthy minimum monthly service charge and I'm trying to save my pennies so I can retire and enjoy the shop.
Any suggestions would be greatly appreciated.
pattenp
Virginia - USA
Light use is vague. The total amps you think you might use at one time is more helpful. With that said I think 2/0-2/0-2/0-1 MHF is probably a good fit for the distance and should handle your needs short of heating and cooling not knowing how big the shop is. The 2/0 aluminum at your distance will handle around 80 amps with allowable voltage drop.
mike93lx
Richmond, VA
I wouldn't go through all that work for anything less than 60a and would be targeting something in the 80-100a range. Secondary service only if it was the only option. Part of the issue there is installation cost. They are likely going to charge you if your load sheet doesn't show any real loads.
laser3kw
northen IL
I have a subpanel feed from a 60amp breaker 75 feet away, buried, sized to handle 100 amp (if needed in future). I have ample lighting (30 t8 tubes) and various intermittent loads - air compressor, welder, lathe, mill. Have not even come close, in 10 years, to needing more.
C
catldavis
Very good info. That's mostly what I will be using - I have a CNC lathe/mill combo, air compressor, welder, car lift, etc. However, can't imagine many will be used at the same time.
mike93lx
Richmond, VA
I bet about max would be hvac running, while you are welding/plasma cutting and your compressor kicks on.
60a really should do just about any one man shop. If you were adding an EV charger, it might be worth increasing that, but charging can done after hours in most cases
laser3kw
northen IL
that's uptown money talk'n right there! :giggle:
seriously, I am accustom to working without in warm months and heating with propane when I'm out there in the winter. Like mentioned, I'm just one guy, and it's unlikely that I would have two high current draw items on at the same time (air compressor and welder)
rancherbill
Foothills County, Alberta, Canada
You know your equipment, and if 60 is good then that's all you need. The only thing that might change is if you source some used 3 phase machining equipment. Three phase stuff is cheaper at the auctions. Who knows what the amps will be so at this point it might be worth doing the 100.
mike93lx
Richmond, VA
Most residential services have HP limits, so if that is the case, the demand can only get so high. That limit seems to often be 7.5-10hp
rancherbill
I don't know, I do not truly understand the magic of VFDs and Rotary Phase Converters. I do know people get smoking hot deals on lathes, mills, etc. because most people do not have three phase power.
mike93lx
Richmond, VA
Sure, but that doesn't necessarily mean high draw. You can do a lot of work with a 3hp motor
C
catldavis
I have another place that has an outside meter can/panel combo (the small house's panel is being used as a sub panel). It's 200 amp service and plenty of space for breakers. If I decide to 3 phase something, I can put a smaller shop there and have plenty power options.
rancherbill
You can easily turn 240 volt single phase (you have it now) into 3 phase power. You need a VFD (Variable Frequency Drive) or a homemade rotary phase converter. You have tons of power in your panel. The amount of power that you actually use in your house is way less than 200 amp. You probably shouldn't have to go to another building to get enough power you probably have enough already.