Subpanel overhead feed?

okrobie

Well-known member
Joined
Jan 4, 2018
Messages
102
Location
Muskogee Oklahoma USA
I want to install a 60A subpanel in my garage, which currently has no power at all. I was planning to dig a trench and lay a 2” sked 40 PVC in the trench as conduit. A friend suggested that I run an overhead conduit from the house to the garage. I don’t know if that would meet code or how to suspend it. The span would be less than 20 feet. Is this a workable solution? Thanks for any suggestions or help. Regards, Jim
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,614
Location
Richmond, VA
No, conduit needs to be properly secured.

Burial is the way to go

2" is way bigger than needed for 60a, but it's a short run, so the added cost won't be earth shattering.
 
OP
O

okrobie

Well-known member
Joined
Jan 4, 2018
Messages
102
Location
Muskogee Oklahoma USA
Thanks Mike and Dave, I’ll probably go for the underground conduit since I’ll probably have other needs such as 10baseT and RG6 as well.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,268
Location
Coastal NJ
Thanks Mike and Dave, I’ll probably go for the underground conduit since I’ll probably have other needs such as 10baseT and RG6 as well.
You mean flooded (submersible) CAT6 not 10 BaseT I hope.
Put some distance between the power and communications conduits.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,761
No, conduit needs to be properly secured.

Burial is the way to go

2" is way bigger than needed for 60a, but it's a short run, so the added cost won't be earth shattering.
2" is around $3 a foot at HD, not cheap like it was before. Being only 20 feet means it won't break the bank.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,614
Location
Richmond, VA
2" is around $3 a foot at HD, not cheap like it was before. Being only 20 feet means it won't break the bank.
Yeah, I know it's gotten stupid. Fittings too.

Personally, I'd run #2 xhhw and 1-1/2 for this. Breaker anywhere between 60 and 90, depending on availability.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,970
Location
Thousand Islands NYS
And I'd run rigid because it only has to be 6" deep. Well worth it to me for my time saved.

PS - my error - rigid metal requires only 6" of cover. PVC requires 18".
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,614
Location
Richmond, VA
And I'd run rigid because it only has to be 6" deep. Well worth it to me for my time saved.

PS - my error - rigid metal requires only 6" of cover. PVC requires 18".
Isnt Florida all sand? Hard to imagine an easier place to dig a trench. Still, 6" deep is easier than 18", no question
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,029
Location
Modesto, CA
I want to install a 60A subpanel in my garage, which currently has no power at all. I was planning to dig a trench and lay a 2” sked 40 PVC in the trench as conduit. A friend suggested that I run an overhead conduit from the house to the garage. I don’t know if that would meet code or how to suspend it. The span would be less than 20 feet. Is this a workable solution? Thanks for any suggestions or help. Regards, Jim
Overhead conduit? How in the world could that be secured?
 
To avoid these ads, REGISTER NOW!

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,289
Location
Illinois near St. Louis, Missouri
Huh? Sch 80 only needed where subject to damage
Problem is "subject to damage" is vague and subject to local interpretation. Everywhere I have lived and done work sch40 was ok for runs on the outside of buildings. But I recall in one county I lived it was very rural and the nearby suppliers were in the next county. When I was looking into what was required for the conduit on the input side of a meter base for underground service I was told it had to be sch80. But that was just that county and didn't apply where I was. Sch40 was considered ok for where I was.
 