Subpanel Puzzler

LOW1

Well-known member
Joined
Jul 20, 2018
Messages
2,643
Location
ontario
i have a 100 amp subpanel in a boathouse. It is fed by a 100 amp GFCI breaker in our cabins main panel.

I was relocating some switches and outlets in the boathouse and tripped the GFCI breaker. so I shut off all breakers in the subpanel including the subpanels main shutoff.

But with everything shutoff in the subpanel I could not get the main panels GFCI breaker to reset.

I found my short, fixed it and now all is well. But why would the GFCI breaker not reset when everything it feeds has been shutoff?
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,813
Location
VT
Did the GFCI trip or did the breaker trip?

If it's not resetting, either the Breaker is bad or your fault is in the line feeding the boathouse. Disconnect the load side of the breaker, does it reset?
 

KenC

Well-known member
Joined
Dec 20, 2009
Messages
2,579
Likely your short was the cause. Leak to ground downstream from the breaker.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,601
Location
Long Island
...I found my short, fixed it and now all is well. But why would the GFCI breaker not reset when everything it feeds has been shutoff?
A neutral-ground connection can trip a GFCI, even when the hot has no power. All you need is a tiny difference in ground voltage between the main and sub-panels (this is normal) for enough N-G current to trip a GFCI.
 
OP
L

LOW1

Well-known member
Joined
Jul 20, 2018
Messages
2,643
Location
ontario
Did the GFCI trip or did the breaker trip?

If it's not resetting, either the Breaker is bad or your fault is in the line feeding the boathouse. Disconnect the load side of the breaker, does it reset?
The breaker in the main panel tripped.

I found the short. It was downstream from the subpanel.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,012
Location
Modesto, CA
remove the wires from the feeder breaker and see if you can reset it. if you can reset it, then shut it off, connect the feeder wires, then try to turn it on. if it trips then you have an issue on your feeder.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,813
Location
VT
The breaker in the main panel tripped.

I found the short. It was downstream from the subpanel.
So it works now?

If not, do as @wyliesdiesels and I suggested.

If it resets you have a short downstream. You can then connect the wires in the main, and disconnect them at the sub (cap the bare wires) to see if it's in that feed or downstream of the sub.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
A neutral-ground connection can trip a GFCI, even when the hot has no power. All you need is a tiny difference in ground voltage between the main and sub-panels (this is normal) for enough N-G current to trip a GFCI.
Not sure I understand the mechanism for this to occur on a non energized circuit. GFCI is not looking for a delta in N-G current but rather a delta in hot to neutral current. Certainly a N-G connection would indeed cause a GFCI to trip on an energized circuit as a difference is created.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,601
Location
Long Island
Not sure I understand the mechanism for this to occur on a non energized circuit. GFCI is not looking for a delta in N-G current but rather a delta in hot to neutral current. Certainly a N-G connection would indeed cause a GFCI to trip on an energized circuit as a difference is created.
If the hot is turned off, it may have zero current flowing through it, but all it takes is 5mA of current flowing through the neutral now to trip a GFCI. And all you need for this to happen is some potential between the ground at the connection downstream of the GFCI, and the neutral-ground bond in the main panel. A volt or two of potential is completely normal (start looking at N-G readings with a DMM), and even galvanic corrosion of the wires acting like a battery can have enough energy to cause the trip.
 