Hello, Currently have 200A main disconnect outside home (this is considered the MAIN PANEL).
From there 4/0 SER AL feeds panel (SUB PANEL) in utility room Siemens 200A, 40 Space.
Would like to run 100A from 200A utility room subale panel to att garage.
Per the NEC 2017; can I run SER AL 1-1-1-3 at the 75C rating due to the terminals rated on panel being 75C, or does it have to be rated at 60C allowable ampacity which would force 1/0 SER AL.
The electrician I had come quote, said I can use SER AL 2-2-2-4 for the 100A subpanel att. gar., but from my understanding this is only good if it feeds the entire 'Dwelling'. I had a second electrician come look, and he said SER 2 AL is fine for 100A sub in att. gar.
From there 4/0 SER AL feeds panel (SUB PANEL) in utility room Siemens 200A, 40 Space.
Would like to run 100A from 200A utility room subale panel to att garage.
Per the NEC 2017; can I run SER AL 1-1-1-3 at the 75C rating due to the terminals rated on panel being 75C, or does it have to be rated at 60C allowable ampacity which would force 1/0 SER AL.
The electrician I had come quote, said I can use SER AL 2-2-2-4 for the 100A subpanel att. gar., but from my understanding this is only good if it feeds the entire 'Dwelling'. I had a second electrician come look, and he said SER 2 AL is fine for 100A sub in att. gar.
Last edited:
WHOOPS. But with your logic, since the inspector passed it, its ok.