Well-known member
Just sold (Pending status) my house and bought a new, to me, place with a 27'x76' pole barn.
Anyhow, had a inspection of my old place and the owners, due to inspection, have asked me to have a licensed electrician look at the subpanel.
I have a small 100 amp subpanel feed by a 100 amp breaker off of the main 200amp panel.
The sub is a old Murry panel located in a room addition to the house and was here when I bougth the home 10 years ago. The panel has two ground/neutral bars stacked on top of each other. The inspector wanted the ground and neutral bars moved. One on the left and one on the right of the breakers. Every panel I have seen has had the two seperate bars connected with a large wire to join the ground and neutral bars on both side of the breakers. So what is wrong with the two bars together in the current location?
Anyhow, had a inspection of my old place and the owners, due to inspection, have asked me to have a licensed electrician look at the subpanel.
I have a small 100 amp subpanel feed by a 100 amp breaker off of the main 200amp panel.
The sub is a old Murry panel located in a room addition to the house and was here when I bougth the home 10 years ago. The panel has two ground/neutral bars stacked on top of each other. The inspector wanted the ground and neutral bars moved. One on the left and one on the right of the breakers. Every panel I have seen has had the two seperate bars connected with a large wire to join the ground and neutral bars on both side of the breakers. So what is wrong with the two bars together in the current location?