Subpanel Question

TravisT

Well-known member
Joined
Oct 22, 2011
Messages
156
Location
NoVA
Trying to plan out some electrical requirements and looking for some feedback. Currently have a 100A subpanel in the 3 car attached garage fed by a 200A main panel. Currently running 2-20A circuits for outlets and a 30 or 40A circuit for a mini-split (have to check, don’t recall). I just bought a Tesla, and need to install the L2 charger. It accepts multiple circuit sizes, but maxes out at 60A.

1. For a 60A circuit run about 50ft from the subpanel, can I run 6 awg thhn in 3/4” conduit, or do I need to bump up to 4 awg? If so, I’ll have to also step to 1” conduit (EMT) I believe.

2. I really had my eyes on one of the EMax compressors (40A circuit) and still need to wire my 220V TIG/plasma circuit. I know I can oversubscribed the subpanel, but I’m not sure by how much given the load types. Do I need to compromise somewhere?
 
To avoid these ads, REGISTER NOW!
OP
T

TravisT

Well-known member
Joined
Oct 22, 2011
Messages
156
Location
NoVA
Thanks for the reply. Maybe I’m reading the documents wrong (see attached). Technically, I think it pulls 48A, but calls for a 60A breaker in the manual along with 6 awg wire, but says to upsize where required. Does the 125% rule still apply?
 

Attachments

  • C9517699-736B-47D7-A62B-16B8015E1F84.jpg
    C9517699-736B-47D7-A62B-16B8015E1F84.jpg
    20.9 KB · Views: 43
OP
T

TravisT

Well-known member
Joined
Oct 22, 2011
Messages
156
Location
NoVA
Sorry about that. Try this one.
 

Attachments

  • Circuit Breaker.pdf
    142.3 KB · Views: 41

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
It looks like they are building the 125% into their installation instructions. If installing for max output, just follow them. I think the "Upsize conductors if necessary" part is about derating for other reasons such as conduit fill.
 
OP
T

TravisT

Well-known member
Joined
Oct 22, 2011
Messages
156
Location
NoVA
That makes sense, and why I wanted to check to get some opinions.

What about voltage drop? Is that a concern with a ~50ft run?

Also, any comments on question #2?
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,271
Location
Penngrove, California
Current Tesla vehicles have a maximum charge rate of 48 Amps, so your 60 Amp circuit is correct, unless there is a chance of a second EV, in which case Tesla Wall Connectors are set up for power sharing, and could make use of the power. Remember the actual charger is in the vehicle, and the vehicle determines rate of charge. There is a reason Tesla calls their EVSE (Electric Vehicle Supply Equipment), a Wall Connector as there is no "charger" in it.

In regard to panel capacity it is all about concurrent use. Most people charge vehicles in "off hours" to make use of time of day billing. You will not use Tig and plasma together, you will use plasma and compressor, and you could have HVAC running. I do not see it likely that you would exceed the 100 Amp breaker for your sub panel, or at least it would be rare.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,256
Location
Modesto, CA
Thanks for the reply. Maybe I’m reading the documents wrong (see attached). Technically, I think it pulls 48A, but calls for a 60A breaker in the manual along with 6 awg wire, but says to upsize where required. Does the 125% rule still apply?

ok so continuous load is 48a, then you apply 125%, which gives you 60a.

youre good to go with #6 THWN in conduit.
 
OP
T

TravisT

Well-known member
Joined
Oct 22, 2011
Messages
156
Location
NoVA
That all makes sense, I guess I was getting hung up on whether the wire had to be 125% of the over current device (60A breaker) or of the actual demand from the device (48A). I would assume if this circuit wasn’t hard-wired to the wall connector, it may be different.

I checked my mini split circuit - it’s 30A. I feel better about not over subscribing the subpanel now, but there is a chance the compressor could kick on while the hvac is on and the car charging. I’ll just have to manage that a little better than I would with a bigger panel.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Your split may not use 30A and how many hp is the comp? Many 5 are now actually 22 run and would almost bet the AC is well under 20. A comp has such a short cycle also. I think you may be able to set the car for 30A service too.
 
OP
T

TravisT

Well-known member
Joined
Oct 22, 2011
Messages
156
Location
NoVA
I believe you’re correct about setting the EV charger to a lower current draw via the wall connector.

You’re also correct that the mini-split likely pulls less than 30A. I would imagine a full current charge to the car and the compressor starting are likely the biggest demands. I think I’ll be good with all I have, and the compressor is a future add, so not even in the equation yet.
 

Noltz

Well-known member
Joined
Mar 10, 2020
Messages
377
Location
Ontario, Canada
My electrician approved 6ga THHN for my 17M run for a Tesla/Other L2 charger. I don't own an EV yet so I installed a 14-50 plug and a 50A breaker for now. That was into 1" PVC conduit, 6-6-6-6.

I think Travis is right and between your Tesla and your AC you'll be close to 80%, but not over, with enough space for your intermittent loads in the garage. But you won't be charging your Tesla while running your AC with your compressor & plasma going. I think that's just simple load management (like not running 2 space heaters on the same 120 circuit). When you're going to play with the plasma cutter, park the Tesla outside.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I have loaded up 100 a lot a couple times, never tripped the main but didnt have a single continuous load of 50 on it. I serviced a bar, tavern, it was astornomical how much was running on 200, they had 5 50A fryers, and the whole rest of the place, probably 30 run air on top of it, coolers, 3 micro, coffee, lights, gobs of s6tuff.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,351
Location
Alexandria, VA
You might want to check prices for 2-2-2-4 AL Mobile Home Feeder or 2-2-2-4 AL SER vs. 6 AWG copper., since MHF and SER is available from so many sources and its relatively cheap. MHF is usually dual rated so it can be run indoors in conduit and also buried outdoors. SER is indoor only and does not require conduit inside. It would require bigger conduit for 2-2-2-4, but you would have no doubts about it handling the current.

Bruce
 
OP
T

TravisT

Well-known member
Joined
Oct 22, 2011
Messages
156
Location
NoVA
I’ll probably stick with the copper route in EMT. Costs a little more, but my run isn’t too long.

One other question - I think I should only need 3x 6 AWG lines since the wall connector only requires L1/L2/G from what I can tell. Can anyone confirm? I can pull a 4th in 3/4” EMT and still be within fill specs I believe, but if the 4th line (N) isn’t necessary, I can cut a little bit of cost there.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,256
Location
Modesto, CA
You might want to check prices for 2-2-2-4 AL Mobile Home Feeder or 2-2-2-4 AL SER vs. 6 AWG copper., since MHF and SER is available from so many sources and its relatively cheap. MHF is usually dual rated so it can be run indoors in conduit and also buried outdoors. SER is indoor only and does not require conduit inside. It would require bigger conduit for 2-2-2-4, but you would have no doubts about it handling the current.

Bruce

SER is permitted for both indoor and outdoor use but can ONLY be used above ground outdoors...
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
12,087
Location
Austin, TX
Note, 6ga is tight in 3/4 if you're pulling 4 wires. If you're pulling just 3, I get it. Make sure it's rated for 60A at appropriate length. If you want us to look at charger spec, post a link.

I'll be very surprised if your mini-split is doing 30 or 40A unless it's multi-head and cooling multiple rooms. My 24k units pull under 15A.. Probably more like 10A.

Doesn't the L2 charger allow you to set charge rate?

Even with everything you've got going on, I think that you'll be fine on 100A. You're concerned about over-subscribing the panel - you can post make/model, but I haven't seen one recently that wouldn't bus 100A.
 
OP
T

TravisT

Well-known member
Joined
Oct 22, 2011
Messages
156
Location
NoVA
The charger specs/manual was attached in post #5:

https://www.garagejournal.com/forum/showpost.php?p=8802803&postcount=5

I haven't put an ammeter on it, but the mini-split called for a 30A breaker. That could have very well been with overhead included. I'm not sure exactly what it pulls, but would also agree it is probably much less than 30A. The mini-split is a 24K BTU and cools either a one-car garage or a 3 car garage, depending on if the door between them is open.

I believe there are a couple of options for charge rates - you can set the circuit size on the charger (from what I understand) as well as the charge rate in the car. I don't have either yet, so I'm not 100%
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
12,087
Location
Austin, TX
The manual referenced doesn't clarify it for me (for certain).. What generation charger is it?
 